Today an inspector told me I cant put a flow and tamper switch on the same zone. My understanding is that they can be on same zone if they provide separate alarm and supervisory annunciation. This is a non addressable system. this is only thing on that zone and is programed waterflow/sup 1st floor. Am I correct???
Top
2017 / 2014 NEC & Related Books and Study Guides
#99233 - 07/31/06 08:28 PM Re: F/A
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
How exactly were you planning to test for all those conditions on two wires of a non-addressable system?
Joe
Top
#99234 - 08/01/06 03:50 PM Re: F/A
energy7 Offline
Member
Registered: 06/10/02
Posts: 58
Loc: Oxnard, CA, USA
They have to be separate or addressible: The tamper is a "trouble" or "supervisory" signal; the water flow is an "alarm" signal.
Top
#99235 - 08/01/06 06:38 PM Re: F/A
sprkrob Offline
Junior Member
Registered: 07/31/06
Posts: 5
Loc: etters,pa,usa
they are not separate but they do send different codes to central monitoring.
the zone is programed waterflow/supervisory.
flow switch sends alarm,tamper sends suprevision,trouble sends trouble.they are separate signals.there is also a separate ground fault LED. there is 2 resistors panel reads them.
Top
#99236 - 08/04/06 08:01 AM Re: F/A
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
sprkrob
Help me out here guy. I've done a fair amount of fire alarm work and I'm at a complete loss as to how you get separate supervisory and alarm indications on a single zone with non addressable equipment.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
#99237 - 08/04/06 08:19 AM Re: F/A
rabbitgun Offline
Member
Registered: 07/25/06
Posts: 23
I've done a bit of FA myself and have never seen this one either. Please post back with the name and model of the panel.
Top
#99238 - 08/04/06 03:41 PM Re: F/A
sprkrob Offline
Junior Member
Registered: 07/31/06
Posts: 5
Loc: etters,pa,usa
OK
the panel reads 4.7K from EOL. You connect WF then 1.1k resistor then tamper then 3.6K then back through NEG. to panel. The panel reads the resistors. Pulls & smokes just have the 4.7 EOL on those zones. If the flow goes it reads 4.7 and goes to alarm. If tamper closes it reads 3.6 and supervision goes .You have to put 1.1 before tamper so panel can't read it. WF is NO, SS is NC. You program these zones to read it this way.
Top
#99239 - 08/04/06 03:47 PM Re: F/A
sprkrob Offline
Junior Member
Registered: 07/31/06
Posts: 5
Loc: etters,pa,usa
OH,
Trouble and supervisory are 2 different signals when programmed this way.
Top
#99240 - 08/04/06 05:30 PM Re: F/A
luckyshadow Offline
Member
Registered: 01/04/05
Posts: 305
Loc: Maryland USA
All I'm going to say is : Thank the powers to be for Addressable systems !!
Beats the hell out of those old hard wired systems.
Top
#99241 - 08/04/06 06:13 PM Re: F/A
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Sprkrob is correct, I have done this in the past also.

I have also just used the tamper (with no reduced resistor) to show an open circuit and activate a trouble/supervisory signal.

I think the inspector is wrong and just not familiar with the installation.

Roger

[This message has been edited by Roger (edited 08-04-2006).]
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 36 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals