The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 236 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#9920 - 05/21/02 08:09 AM Help finding code reference.
Switcher Offline
Junior Member

Registered: 04/29/02
Posts: 9
Loc: Charlotte NC
In gound well pumps (sprinkler system) and GFCI protection, any code reference would be appreciated, haven't been able to find anything specific.

Want to make sure GFCI is not required.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#9921 - 05/21/02 08:21 AM Re: Help finding code reference.
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
GFCI rules are found in 210-8. You did not say if this was residential/commercial, or if the source was outside/inside. If you are utilizing a 110 volt outlet outside, I'd say yes it is required, other than that, need more info.

Top
#9922 - 05/21/02 08:51 AM Re: Help finding code reference.
Switcher Offline
Junior Member

Registered: 04/29/02
Posts: 9
Loc: Charlotte NC
This is a residential well to be fed from indoor subpanel with UF cable.

Well will have submersible pump and will be strictly for yard sprinkler system.

I am assuming it will be 240 volt but possible that it will be 120V, haven't seen it yet.

Just want to know if there is a firm rule/code section requiring GFCI for these applications.

Top
#9923 - 05/21/02 06:00 PM Re: Help finding code reference.
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use

Exception No. 1: Receptacles that are not readily accessible.
Exception No. 2: A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8).



(3) Outdoors
Exception: Receptacles that are not readily accessible and are supplied by a dedicated branch circuit for electric snow-melting or deicing equipment shall be permitted to be installed in accordance with the applicable provisions of Article 426.



(4) Crawl spaces — at or below grade level
(5) Unfinished basements — for purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like
Exception No. 1: Receptacles that are not readily accessible.['i]
[i]Exception No. 2: A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8).

Exception No. 3: A receptacle supplying only a permanently installed fire alarm or burglar alarm system shall not be required to have ground-fault circuit-interrupter protection.




(6) Kitchens — where the receptacles are installed to serve the countertop surfaces

(7) Wet bar sinks — where the receptacles are installed to serve the countertop surfaces and are located within 1.8 m (6 ft) of the outside edge of the wet bar sink.

(8) Boathouses

Top
#9924 - 05/24/02 07:30 PM Re: Help finding code reference.
hurk27 Offline
Member

Registered: 05/15/02
Posts: 71
Loc: Portage, Indiana
There is no code even if the pump was fed by a recptical as long as its a single it would be covered by a dedacated circuit/perment in place rule if there is any metel piping or casing make sure there is a egc ran to it
:Wayne
_________________________
Be Fair, Be Safe
Just don't be Fairly Safe

Top