#99144 - 07/23/06 05:31 PM GFCIs in one room controlling loads elsewhere.
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
Since GFCI receptacles are now quite reasonably priced might it be time for code language that requires GFCI receptacles to be in the same room as any other receptacles they control? Note that I'm only talking about GFCI receptacles and not breakers. I'll admit to being ambivalent about the blank face GFCIs. Can anyone think of a reason not to have them under the same restriction. Be advised that I'm not referring to the ones placed for serving pools.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
2017 / 2014 NEC & Related Books and Study Guides
#99145 - 07/23/06 05:36 PM Re: GFCIs in one room controlling loads elsewhere.
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Makes sense to me!
Top
#99146 - 07/23/06 05:59 PM Re: GFCIs in one room controlling loads elsewhere.
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Sounds to me like......
Exterior, garage, basement (unfin), bathrooms, etc.
A great step forward for convenience, although the 'code' is not convenient.

Also would be a blessing for us AHJ's, save a lot of trips up & down the stairs. Heck, I may have to sign-up at a gym!

John

PS: All kidding aside, it's a good thought.
_________________________
John
Top
#99147 - 07/24/06 02:02 AM Re: GFCIs in one room controlling loads elsewhere.
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
In my opinion it is a design decision.

Are we also going to require the branch circuit OCPD to be located in the room it serves?

Same inconvenience and safety issues.

As it happens we very rarely 'load side' any GFCIs, most of the prints we get show a separate GFCI at each point of use. But why take away options if mealy for convenience.

Plus this keeps John out of the gym.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#99148 - 07/24/06 04:29 AM Re: GFCIs in one room controlling loads elsewhere.
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
The NEC is a minimal code standard, intent upon listing minimal standards for the safe operation of electrical systems. It would exceed the stated purpose of the NEC to require the use of receptacle type GFCI devices in every outlet requiring GFCI protection.

Go for it if you want, I do.
_________________________
Earl
Top
#99149 - 07/24/06 09:21 AM Re: GFCIs in one room controlling loads elsewhere.
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
If nothing changes in the ROC we are going to have AFCIs on all the 120v circuits anyway so a tripped GFCI will be the least of your worries. The NFPA/government is out of control.
_________________________
Greg Fretwell
Top
#99150 - 07/24/06 01:28 PM Re: GFCIs in one room controlling loads elsewhere.
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
gfretwell Wrote:
Quote:
If nothing changes in the ROC we are going to have AFCIs on all the 120v circuits anyway so a tripped GFCI will be the least of your worries. The NFPA/government is out of control.
Sir
You have that right! They reject common sense proposals such as changing the name of the "Equipment Grounding Conductor" to "Equipment bonding Conductor" But they let manufacturers jam this cure in search of a disease down our throats. We are going to have to fight that particular battle state by state and locality by locality. They are going to begin reversing the progress that was being made to standardize codes across jurisdictions and return to the balkanization effect of yesteryear.
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals