ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 255 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#99097 07/15/06 12:47 AM
Joined: Jul 2006
Posts: 1
M
miguel Offline OP
Junior Member
At work while i was troubleshooting a UPS system i noticed that i was not getting an output supply 240 volt i was only getting 120 volts. When i checked the transformer for this system i observed that it needed a 480 volt 3 wire input supply in order to get a 120/240 volt, but the input supply was a single phase 240 volt supply. i am certain that is the main reason why i am not getting 240 volts from this UPS. I WANT TO KNOW IF THERE IS A WAY TO CONFIGURE THE TRANSFORMER TO WORK WITH A SINGLE PHASE 240 VOLTS 3 WIRE INPUT AND STILL BE ABLE TO GET A 120/240 VOLT OUTPUT FROM THIS SYSTEM? i have some spec diagrams i have scanned but i don't know how to post them on this site. IF you're interested in seeing the transformer spec diagrams email me at amnottall@yahoo.com and i'll email it to you.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Miguel,

Welcome to ECN.

I have a few questions regarding the UPS:

Quote

it needed a 480 volt 3 wire input

Is this 3 Wire Input 480 VAC 3 Phase 3 Wire, or 480 VAC 1 Phase 2 Wire + Equipment Grounding Conductor?

3 Phase 3 Wire Input would have 3 individual terminals on the Primary Side of the Transformer, most likely marked "H1", "H2" and "H3".
There would also be a Lug on the Enclosure, where the "EGC" (Equipment Grounding Conductor) would be terminated at.

1 Phase 2 Wire Input would have only 2 terminals on the Primary Side, and may be marked as "H1" and "H2".
The ECG would terminate to a Lug on the Enclosure, or possibly to a Lug on a Terminal Strip inside of a "Cabinet".
The EGC's Lug / Terminal would be Colored Green, or identified with a "Ground" symbol.

Quote

I WANT TO KNOW IF THERE IS A WAY TO CONFIGURE THE TRANSFORMER TO WORK WITH A SINGLE PHASE 240 VOLTS 3 WIRE INPUT AND STILL BE ABLE TO GET A 120/240 VOLT OUTPUT FROM THIS SYSTEM?

First off, _ONLY IF_ the Primary Windings are "Split Coil", and the Primary Side terminations have factory provisions, which allow the Primary Windings to be connected in either Series (480V), or Parallel (240V), the UPS may be used on a 240 VAC System.

If there is no "Input Voltage Changing Provisions" - such as reconfigurable jumpers, etc., then the UPS can only be used with a 480 VAC Input.

Secondly, you mention "A SINGLE PHASE 240 VOLTS 3 WIRE INPUT":

If by this you mean the input Circuitry has 2 Ungrounded Conductors + 1 Grounded "Neutral" Conductor, this may be an incorrect way to feed the UPS - especially if the Primary Windings are Isolated from the Secondary Windings.
If this Circuit is a 240 VAC Single Phase Circuit, the Primary side would only accept 2 Ungrounded Conductors.

If you mean the input is from a 240 VAC 3 Phase 3 Wire Circuit - such as from a 240 VAC 3 Phase 3 Wire Delta System, or a 240/120 VAC 3 Phase 4 Wire Delta System, or even a 208Y/120 VAC 3 Phase 4 Wire System, you have a 3 Phase Power System.
This would be a Circuit with 3 ungrounded Conductors, or a System with 3 "Active Circuit" Conductors having the same Voltage measured across them - as measured between "A-B", "B-C" and "A-C".

Another question regards the Secondary Side's Grounding Electrode System.
If this UPS _IS_ an Isolated Transformer type, the "Output" should be bonded to a Grounding Electrode System - actually the one used with the Utility Supplied Power System on-site.

Way too many questions / scenarios regarding this UPS setup - best if you contact the manufacturer for details.

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Nov 2005
Posts: 827
Likes: 1
J
Member
The input to your UPS doesn't need to have any specific relationship to the output, other than the power in capability >= the power out plus conversion losses. It is the Alternate Source input that has to be compatable with the UPS output. For instance, I maintain UPS systems with a 120/208 3 phase rectifier input. The output is 120 single phase. The alternate source input is 120 single phase. The inverter phase locks to the alternate source. Two sets of inverse parallel SCRs called the "Static Bypass Switch", provide uninterrupted switching to the alternate source should inverter problems arise. It would be unusual for a UPS to have a center tapped output because the Static Bypass would require 8 SCRs instead of 4. The manufacturer would probably tell you to use a transformer on the output for 120/240.
Joe

By the way, I have fixed many types of UPS failures. I have never had one re-configure itself. I don't think that you have either. So the question becomes, "Who changed something external, and how do you put it back?



[This message has been edited by JoeTestingEngr (edited 07-16-2006).]


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5