#99082 - 07/13/06 05:07 PM How many bathrooms on one circuit?
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
When I'm feeling thrifty.... I often hit say a master, guest, and powder room with one circuit for just the recepticals. Lighting on an adjoining room if loads allow. Anything wrong with that?

Quote:
210.11(C)(3) Bathroom Branch Circuits.
In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply the bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A).
FPN:See Examples D1(A), D1(B), D2(B), and D4(A) in Annex D.


Or have I read this wrong?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
2017 / 2014 NEC & Related Books and Study Guides
#99083 - 07/13/06 06:29 PM Re: How many bathrooms on one circuit?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Bill Gates could have all 27 bathrooms in his house on one GFCI 20 if he was only serving the receptacles.
That is a design issue.
_________________________
Greg Fretwell
Top
#99084 - 07/13/06 06:59 PM Re: How many bathrooms on one circuit?
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
I see nothing wrong codewise. It is the bare minimum required by the code. However, a line-load design with GFCI device in the basement, and the master bathroom on 2nd floor, is a poor, poor design.
Top
#99085 - 07/14/06 04:39 AM Re: How many bathrooms on one circuit?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Ron:
IF you are saying a GFI receptacle in the basement, then up to the baths, that buys a red sticker. If you are saying a faceless GFI in basement then I say "BAD design", but compliant.

John
_________________________
John
Top
#99086 - 07/14/06 07:56 AM Re: How many bathrooms on one circuit?
trobb Offline
Member
Registered: 06/08/06
Posts: 110
Loc: Iowa City, IA
I know that where I come from (Cedar Rapids, Iowa) you cannot have wiring from the basement (etc) additionally serving another floor, stairs exempt. It is a mod the city added to the NEC.
(Sidenote: A nice thing they also added is that panels in a residence cannot be closer than 6" to a corner. Makes for easier access)
Edited for better wording.

[This message has been edited by trobb (edited 07-14-2006).]
Top
#99087 - 07/14/06 08:18 AM Re: How many bathrooms on one circuit?
XtheEdgeX Offline
Member
Registered: 04/17/05
Posts: 116
Loc: Florida
As the code section you referenced states,
You are not allowed to add receptacles from other rooms onto the circuit that feeds the bathroom receptacles.
Top
#99088 - 07/14/06 10:21 AM Re: How many bathrooms on one circuit?
Trick440 Offline
Member
Registered: 08/15/05
Posts: 247
Loc: Waterford, MI, USA
Heres the right way to do it.

HR for bath plugs goes in the master bedroom. You can jump out of that the feed another bathrooms plugs.

Depending on if there is alot of plugs in the master, multiple bathrooms, etc. We will pull another circuit for other bathrooms. Hair dryers are pulling alot of amps these days.

The 20amp circuit is only for bath plugs. Lighting is pulled from any general circuit.

So E, your right. Bigger houses you might wanna ppull 2 , 20 amp circuits for plugs.

[This message has been edited by Trick440 (edited 07-14-2006).]
_________________________
Shake n Bake
Top
#99089 - 07/14/06 03:58 PM Re: How many bathrooms on one circuit?
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
I am quite familiar with the practice of having all bath receptacles, in all baths, on one circuit, protected by a GFI receptacle in the first bath the cirrcuit reaches. "Economy" is always cited as a reason for this.

I question that reasoning.

Sure, it makes sense in tract homes of the "1970's" style. In those homes, the design usually had all the plumbing grouped together, so baths were either back-to-back or directly above one another.

Yet, I have just come from a new home in the "Courtyard" style. This style has the rooms arranged in a box, around an inner courtyard. There were five baths, including eight receptacles , scatttered around this square, and on two levels. One GFI receptacle protected them all.

That is a lot of wire to loop around, up, and down. Apart from the wire cost, there is the labor involved. Compare that to using a multi-wire branch circuit, with one leg for the neighboring room, and one for the bath- and each bath having its' own GFI.

Since, in realtive terms, the cost of GFI's has dropped- I think saving $$$$ by eliminating $10 devices is often false savings!

(This can also be another reason in favor of AFCI devices!)
Top
#99090 - 07/14/06 04:26 PM Re: How many bathrooms on one circuit?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Although NEC compliant, and INHO poor design practice one 20 amp circuit for ALL baths is a PITA. Not the GFI tripping, but the 20 amp CB tripping from more than one blow dryer on.

It's a pain in the butt as AHJ, GFI in first floor powder room & 3 or 4 baths upstairs.

But, alas, it's compliant!!

John
_________________________
John
Top
#99091 - 07/14/06 07:13 PM Re: How many bathrooms on one circuit?
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Actually, John - and I should have clarified - what I meant was that the GFCI device would be in a downstairs (maybe basement level) bathroom with no other loads feeding receptacles in other bathrooms. I despise doing it like that but my boss demands it because of $$$. At the very least, elimanate the line-load design and install devices in each bathroom to avoid the nuisance of going down flights of stairs in order to reset the GFCI.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals