The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 11:48 AM
100% breakers?
by gfretwell
01/14/17 08:10 PM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 10
Trumpy 8
Who's Online
1 registered (geoff in UK), 255 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99075 - 07/13/06 04:11 PM Dedicated Space Question
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Does 110.26(F) apply to a anything else besides the item listed in the article?

Second question - Does 110.26(A) apply to J-boxes?
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#99076 - 07/13/06 04:20 PM Re: Dedicated Space Question
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
How would you do the Job?? Just items mentioned in code section I;d say. Nope/\

Top
#99077 - 07/13/06 07:17 PM Re: Dedicated Space Question
Celtic Offline
Member

Registered: 02/26/05
Posts: 367
Loc: NJ
Where are you heading with this?
_________________________
~~ CELTIC ~~
...-= NJ =-...

Top
#99078 - 07/13/06 08:39 PM Re: Dedicated Space Question
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
"Sufficient access and working space shall be provided and maintained about all electric equipment to permit ready and safe operation and maintenance of such equipment."

Is what it says first, and later lists the parameters....

"Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized..." - You can shut off a box, and it very unlikely that you would need to do all of those things hot, like you might for a panel, especially a main panel. As far as "F" goes, I (Can't) think of anything else...

[This message has been edited by e57 (edited 07-14-2006).]
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#99079 - 07/13/06 09:14 PM Re: Dedicated Space Question
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9058
Loc: Estero,Fl,usa
I never quite understood why an HVAC disconnect needed to be serviced while energized but I have always been told it needed full working space.
If we changed the rule on that the world would spin out of orbit, into the universe and life as we know it would cease ... or so we have been led to believe.
_________________________
Greg Fretwell

Top
#99080 - 07/13/06 09:23 PM Re: Dedicated Space Question
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9058
Loc: Estero,Fl,usa
I just popped up the same question over at the IAEI board. Lets see what they say
_________________________
Greg Fretwell

Top
#99081 - 07/14/06 05:49 AM Re: Dedicated Space Question
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
As E57 refers to; does it need servicing, adjustment, etc. while energized ?
A large J box with contactors in it or something like that would be a yes, otherwise no.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.