#98999 - 07/05/06 04:13 PM Generator v. SDS
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Is it just me or are others wrestling with Kohler about how to lift the bonding on their generators so they can be used with the "neutral" on bonded at the generator? The reason for the question is I am seeing small generators (10 kw) 120/240 single phase generators coming from the factory with a tag on the generator indicating the neutral is bonded to the frame of the generator and that it can be removed in the field for applications where it should not be bonded. Example: Back up generator permanently installed using a 2 pole transfer switch. The neutral is bonded to the frame of the generator and the neutral of the utility is also bonded at a different location. Now we all know the rules about bonding the neutral in two places and this scenario is a violation. Now here's the hook- Kohler tells you that the neutral is bonded to the frame but they don't tell you how to lift the bond or where the bond is. I can read specs and prints and they are silent about this bonding or shall I say un-bonding.
It is standard procedure for Kolher to bond the neutral to the frame at the factory for testing and they always ship them out from the factory with the neutral bonded to the frames and as such they are separately derived systems.

Maybe the title should be SDS v. Not

[This message has been edited by George Little (edited 07-05-2006).]
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#99000 - 07/05/06 07:23 PM Re: Generator v. SDS
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
George
The Generator folks I;ve worked with say they send them out that way because there not sure if they'll be hooked up as a Seperately derived system or not so they can be corrected in the field if required. Such as 3 phase 4 wire with a 4 pole is a S.D. system 3 phase 4 wire with a 3 pole transfer switch is not.Depends on the transfer switch in each case.
Yoopersup
Top
#99001 - 07/05/06 07:27 PM Re: Generator v. SDS
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
George
The Generator folks I;ve worked with say they send them out that way because there not sure if they'll be hooked up as a Seperately derived system or not so they can be corrected in the field if required. Such as 3 phase 4 wire with a 4 pole is a S.D. system 3 phase 4 wire with a 3 pole transfer switch is not.Depends on the transfer switch in each case.
Yoopersup
Top
#99002 - 07/05/06 07:36 PM Re: Generator v. SDS
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Ernie, I don't have a problem with that- Sending them out that way, but Kohler don't tell you anything about where the jumper is or what to do to change it. They only show a skimpy block diagram of the components and nothing about any bonding jumper. I've always thought of Kohler as a rather reputable company but I'm having second thoughts now since their technical support is so lax. Generac and Onan know how to handle this situation so they get my vote.
_________________________
George Little
Top
#99003 - 07/05/06 08:04 PM Re: Generator v. SDS
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I spent some time on the web site and this is not in any of the PDFs about installation.
Have you tried asking the tech support?
I think this should be on a big label somewhere.
_________________________
Greg Fretwell
Top
#99004 - 07/05/06 10:22 PM Re: Generator v. SDS
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
for 10 KW Kolher generators the bonding strap will be loacted in main control panel near the circuit breaker you will see the netural termail strip it is small wire or band.

that where the bonding strap will be located

but for other generator manufacter it is straght foward job i useally ask them in ahead of time and they will do it before they arrive in the site or location where the generator will be at and i just make quick look to double check make sure doing the proper way

Merci , Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by sparkyinak
01/24/17 02:04 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
3 registered (Admin, sparkyinak, Ruben Rocha), 119 Guests and 16 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals