#98873 - 06/20/06 02:12 PM ground loops
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
I had an engineer tell me today that a tankless hot water heater with sensitive electronic controls was not operating properly because a 'second ground' run thru a correctly installed emt was connected directly to the neutral bus in the service panel and not to a separate ground bus. He understands the two busses connect directly to one another in the panel, but he says it makes a difference and can create a ground loop which affects the point of reference of the electronic controls at the unit.

Could a foot and a half of #4 really make a difference? Maybe this should be in the technical area, but I was having trouble getting that one up.
Top
2017 / 2014 NEC & Related Books and Study Guides
#98874 - 06/20/06 02:19 PM Re: ground loops
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Sounds pretty shaky to me
_________________________
Greg Fretwell
Top
#98875 - 06/20/06 02:35 PM Re: ground loops
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
Is there a significant amount of current running thru this 'second ground' wire? If so, is the temperature sensor wiring wrapped around this current carrying wire?

LarryC
Top
#98876 - 06/20/06 03:30 PM Re: ground loops
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
Sounds like a shipment of male bovine excrement to me.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#98877 - 06/20/06 04:10 PM Re: ground loops
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
To add: I'd be willing to move the redundant ground to the other bus just to shut him up (meaning call his bluff).
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#98878 - 06/20/06 05:58 PM Re: ground loops
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
If there is a ground loop it is in his equipment not your wiring. There should be no way a "ground loop" in the line side of any equipment should affect the "data" side. He may have something grounded that shouldn't be but it is not in an article 300 wiring method. It is in his LAN or internal wiring.
_________________________
Greg Fretwell
Top
#98879 - 06/20/06 06:27 PM Re: ground loops
Steve T Offline
Member
Registered: 02/14/01
Posts: 306
Loc: Oak Park, IL, USA
Thanks. I tend to agree with you guys, but this guy says their company does a lot of engineering for sensitive equipment--Honeywell and some others-- and says somethings dealing with inductance, capacitance (unspecific) he may not have known exactly, can cause this situation. When they removed the second ground all together, the unit works fine.

Like I said, I don't see how a short piece of wire can change all of this (especially when it is a #4 in a 200amp panel or a direct connection thru the panel enclosure itself) I guess I'd need to see the technical specs.

He said they were measuring a 1/2 amp on the ground wire. I don't know how they know there isn't current on the conduit.

Where's Scott? He usually has a complex answer.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 121 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals