ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 16
Recent Posts
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
TRUE POWER
by jraef. 03/21/17 09:13 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,407 Are you busy
166,131 Re: Forum
160,590 Need opinion
Who's Online Now
0 registered members (), 50 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#98873 - 06/20/06 05:12 PM ground loops  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
I had an engineer tell me today that a tankless hot water heater with sensitive electronic controls was not operating properly because a 'second ground' run thru a correctly installed emt was connected directly to the neutral bus in the service panel and not to a separate ground bus. He understands the two busses connect directly to one another in the panel, but he says it makes a difference and can create a ground loop which affects the point of reference of the electronic controls at the unit.

Could a foot and a half of #4 really make a difference? Maybe this should be in the technical area, but I was having trouble getting that one up.


2017 / 2014 NEC & Related Books and Study Guides

#98874 - 06/20/06 05:19 PM Re: ground loops  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,057
Estero,Fl,usa
Sounds pretty shaky to me


Greg Fretwell

#98875 - 06/20/06 05:35 PM Re: ground loops  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 781
Winchester, NH, US
Is there a significant amount of current running thru this 'second ground' wire? If so, is the temperature sensor wiring wrapped around this current carrying wire?

LarryC


#98876 - 06/20/06 06:30 PM Re: ground loops  
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Sounds like a shipment of male bovine excrement to me.


Larry Fine
Fine Electric Co.
fineelectricco.com

#98877 - 06/20/06 07:10 PM Re: ground loops  
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
To add: I'd be willing to move the redundant ground to the other bus just to shut him up (meaning call his bluff).


Larry Fine
Fine Electric Co.
fineelectricco.com

#98878 - 06/20/06 08:58 PM Re: ground loops  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,057
Estero,Fl,usa
If there is a ground loop it is in his equipment not your wiring. There should be no way a "ground loop" in the line side of any equipment should affect the "data" side. He may have something grounded that shouldn't be but it is not in an article 300 wiring method. It is in his LAN or internal wiring.


Greg Fretwell

#98879 - 06/20/06 09:27 PM Re: ground loops  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
Thanks. I tend to agree with you guys, but this guy says their company does a lot of engineering for sensitive equipment--Honeywell and some others-- and says somethings dealing with inductance, capacitance (unspecific) he may not have known exactly, can cause this situation. When they removed the second ground all together, the unit works fine.

Like I said, I don't see how a short piece of wire can change all of this (especially when it is a #4 in a 200amp panel or a direct connection thru the panel enclosure itself) I guess I'd need to see the technical specs.

He said they were measuring a 1/2 amp on the ground wire. I don't know how they know there isn't current on the conduit.

Where's Scott? He usually has a complex answer.



Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.7825 MB (Peak: 0.9349 MB) Zlib enabled. Server Time: 2017-03-25 11:37:50 UTC