#98838 - 06/15/06 06:18 PM water main
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
It's been a while since I have done a 200 amp service, I'll be using 4/0 AL for service. #6 to ground rods. Does the water main get #4 ? Sorry to sound stupid just having one of those days.
Top
2017 / 2014 NEC & Related Books and Study Guides
#98839 - 06/15/06 06:48 PM Re: water main
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
6 for the ground is ok check 250.66
Top
#98840 - 06/15/06 06:56 PM Re: water main
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
250.66 says 4/0 AL with copper ground is #4. Or am I reading wrong?
Top
#98841 - 06/15/06 07:16 PM Re: water main
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
#4 copper to the water main will be fine, and meets code per NEC.
Top
#98842 - 06/15/06 07:29 PM Re: water main
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
If I can run a #6 I will do that any wire I do not have to buy at these prices will help.
Top
#98843 - 06/15/06 07:37 PM Re: water main
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The ground rod conductor can be #6 but you still have to bond the pipe with #4.
_________________________
Greg Fretwell
Top
#98844 - 06/16/06 06:38 AM Re: water main
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
oppps


I didn't catch the reference to the water pipe. Sorry

as gfretwell stated.
Interior water pipe requires a # 4 The rods are fine with the #6.


Sorry again


Charlie
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals