The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 201 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#98790 - 06/07/06 03:39 AM fire rated walls/ceilings
gserve Offline
Member

Registered: 03/11/03
Posts: 92
Can plastic boxes be used in these areas?

Top
2014 / 2011 NEC & Related Books and Study Guides
#98791 - 06/07/06 05:09 AM Re: fire rated walls/ceilings
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Yes, see the UL listing(s)for the boxes in question.

Roger

Top
#98792 - 06/07/06 06:27 AM Re: fire rated walls/ceilings
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
One could also look inside the boxes and in most cases it will have lettering that will say "2 HR W C". In that case it would be suitable for a 2 hour rating in a wall or ceiling. I would qualify my statment by saying that is what I typically see in a non-metalic box used for NM cable. There would possibly be other ratings for other boxes.

typo's

[This message has been edited by George Little (edited 06-07-2006).]
_________________________
George Little

Top
#98793 - 06/07/06 02:12 PM Re: fire rated walls/ceilings
gserve Offline
Member

Registered: 03/11/03
Posts: 92
Thanks for the info. Now how about the cover? I need to use a blank plate on a round plastic nail-on box. I looked at the Arlington plastic blank plate and I don't see a rating on it. Do I need to use a metal blank-up plate? I rather use the pastic one it is white like the ceiling.

Top
#98794 - 06/07/06 03:09 PM Re: fire rated walls/ceilings
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Gserve:
Just had this discussion with UL (Northbrook, Il) today, regarding 'extensions' in fire rated ceiling.

Per the White Book, 'ANY' type of plate can be installed on the rated boxes, as long as the boxes are installed to mfg/UL specs.

My inquiry related to extensions on deep set boxes, 2 hr rated ceiling; answer was yes, Arlington BE-1R is OK (4" round), but, BE-1 for 1-gang device is not. Go figure??

John
_________________________
John