#98754 - 06/04/06 08:02 PM Bonding per 680.26(C)  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Are the lugs and screws that are installed on pool & spa equipment by the factory suitable for bonding the equipment to the bonding grid? Do inspectors ask that the contractors replace these lugs and screws with ones made of stainless steel, brass or copper or other non-corrosive material?


George Little

2017 / 2014 NEC & Related Books and Study Guides

#98755 - 06/04/06 09:39 PM Re: Bonding per 680.26(C)  
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Yes, and they shouldn't.


Larry Fine
Fine Electric Co.
fineelectricco.com

#98756 - 06/05/06 06:20 PM Re: Bonding per 680.26(C)  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,798
Brick, NJ USA
George:
I have to agree with Larry
Yes, and why are they requested/required to be replaced??

John


John

#98757 - 06/05/06 09:15 PM Re: Bonding per 680.26(C)  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
John & Larry- I agree with you guys and so does UL. Once you start altering a UL Listed equipment you are inviting problems. The equipment is Listed with the lugs on it and that's where we connect the Bond wire. But, we still have some inspectors out there that read the wording about brass, copper or stainless connections and they have the contractors changing them. I say they are wrong for doing so.


George Little

#98758 - 06/06/06 06:09 PM Re: Bonding per 680.26(C)  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,798
Brick, NJ USA
George:
Perhaps it's time for a little CE or Seminar on Article 680??

Only mention of the SS, Brass of Cu lugs that I'm aware of regards bonding IG???

Maybe I missed something??

John


John