The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#98725 - 02/24/05 06:52 PM 210.4(B)
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Now we are required to use a means to disconnect(at the circuit origin) all ungrounded conductors at the same time for multiwire circuits feeding the same yoke in other that dwellings.(210.4(B)2005 NEC)

shortcircuit

Top
2014 / 2011 NEC & Related Books and Study Guides
#98726 - 02/25/05 04:54 PM Re: 210.4(B)
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
That is no change.
_________________________
Earl

Top
#98727 - 02/25/05 06:05 PM Re: 210.4(B)
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The change is they expanded the rule beyond "dwelling units".