The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Topic Options
Rate This Topic
#98678 - 02/17/05 04:19 PM Grounding of ranges
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Does 250.140 exception(2005 NEC) allow the extension of a exsisting type SE service-entrance cable feeding a range to a new location in a kitchen remodel in a dwelling by installing a juction box, which is grounded with the SE, extending the supply circuit(with SE) to the new location of the range, and grounding of the range with the SE cables grounded circuit conductor as it was originally installed?

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#98679 - 02/18/05 09:52 AM Re: Grounding of ranges
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I don't see that directly addressed but it does sound reasonable that if you can use an existing 3 wire circuit you can extend it.
I think that if replacement is practical it should be done but I also understand that can be an unreasonable burden in old work.
_________________________
Greg Fretwell
Top
#98680 - 02/19/05 03:53 AM Re: Grounding of ranges
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Shortcircuit IMO extending that circuit is not allowed by Rule 3 of our (MA) 527 CMR 12:00: 2005 MEC.

Quote:
Rule 3. Additions or modifications to an existing installation shall be made in accordance with this Code without bringing the remaining part of the installation into compliance with the requirements of this Code. The installation shall not create a violation of this Code, nor shall it increase the magnitude of an existing violation.


I do not know anyway you can add to this circuit and meet the new code.

As an example can you add a grounding receptacle to a K&T system?

Also IMO the NEC will not allow what you are asking about, the new location for the range is just that a new location / installation.

IMO existing as used by NEC 250.140 exception means where it is now, not where you want to move it.

Bob


[This message has been edited by iwire (edited 02-19-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#98681 - 02/19/05 05:15 AM Re: Grounding of ranges
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
The only way I have done this is if the wire reaches to the new location of the range which is usually a few feet to the left or right. If it does not I run a new circuit.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 117 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals