The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (LongRunner), 232 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#98543 - 06/01/06 09:31 AM code reference please
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Can someone refer me to the section where I can run from 1 bath room to the second provided no other loads attached.I`m refering to the 20 amp recp. Is it 210.11c3? It doesn`t come out and say that you can run from one bath to the other if nothing else is attached to it.I know if lites or other loads are used it`s only allowed to serve that bathroom.I have this GC that wants to see it.And after reading it it isn`t all that clear here I guess the word ( outlet)s is the key?Thanks in advance

Top
2014 / 2011 NEC & Related Books and Study Guides
#98544 - 06/01/06 10:15 AM Re: code reference please
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Reel-Break, you are correct, it is 210.11(C)(3).

 Quote:
(3) Bathroom Branch Circuits In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s).
This sentence does not prohibit receptacles in more than one bathroom from being supplied from the one "bathroom receptacle branch circuit"
 Quote:
Such circuits shall have no other outlets.
This sentence would prohibit outlets other than bathroom outlets from being supplied by the "bathroom receptacle branch circuit" or circuits if you chose to install a circuit per bathroom..

 Quote:
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).
This exception makes it clear that the circuit could supply receptacle outlets in more than one bathroom, but if the circuit supplies lighting outlets as well, it would be necessary to limit it to a single bathroom.

Roger

Top
#98545 - 06/01/06 03:16 PM Re: code reference please
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Interesting subject.

I dislike what the code allows here. I believe it's a horrible design to have one GFCI device control an additional receptacle even if the other recpetacle (that's protected by the GFCI device) is on a different level of the dwelling.

It's a design issue in my opinion.

Top
#98546 - 06/01/06 03:29 PM Re: code reference please
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
I don't necessarily disagree, but I imagine that the survivor of a real-world GFCI-tripping event would not have convenience be their primary concern.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#98547 - 06/01/06 03:31 PM Re: code reference please
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Upon further thought, would you insist on having a sub-panel on every level of a house?
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#98548 - 06/01/06 03:37 PM Re: code reference please
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
There is nothing requiring a GFCI circuit, individual GFCI receptacles can be installed in each bathroom.

Roger

Top
#98549 - 06/01/06 04:59 PM Re: code reference please
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Basically the quantity of GFCI receptacles within the bathrooms of a McMansion are dependent on $$$$$$$$.

Four bath house, GFI in powder room, branch to #1, branch to #2, and then to Master with 2 receptacles.

Same basic house, 'custom builder', GFI in each bath, still one circuit.

Larger McMansion, 2 powder, 4 full, & huge master....direct line and GFI in EACH.

Kitchens vary also, from basic two GFI's to all GFI's.

It's design, it's spec, it's all NEC compliant, and it's ALL $$$$$$

John
_________________________
John

Top
#98550 - 06/02/06 05:57 AM Re: code reference please
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
 Quote:
Larger McMansion, 2 powder, 4 full, & huge master....direct line and GFI in EACH.


Is that where Ronald McDonald lives?
_________________________
Ryan Jackson,
Salt Lake City

Top
#98551 - 06/02/06 06:53 AM Re: code reference please
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
If I were you I would not run from the load side of the first bath room but run it from the line side. Then the home owner won`t have to run into the other bath to reset it.

Top
#98552 - 06/02/06 12:08 PM Re: code reference please
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
You do realize that you would lose the GFCI protection by feeding the second bathroom's receptacle outlet from the line side of the GFCI receptacle, don't you?
_________________________
Earl

Top