The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
sparky 4
Who's Online
1 registered (Radar), 321 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#98540 - 05/31/06 07:32 PM GEC sizing
hedlok Offline
Junior Member

Registered: 03/25/06
Posts: 8
Loc: pa.
200A service with 4/0 alum. cond. what size GEC is okay? i know that table 250.66 says #4 but im in an arguement with someone who says it's not required to be any larger than #6. also, there is no rebar ground and plastic water service. what do you say?

2014 / 2011 NEC & Related Books and Study Guides
#98541 - 05/31/06 07:43 PM Re: GEC sizing
Bob Offline

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
250.66(A) says #6.

#98542 - 05/31/06 08:35 PM Re: GEC sizing
Larry Fine Offline

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
A driven ground never needs more than #6 cu. Any other electrode, #4 cu.