#98540 - 05/31/06 07:32 PM GEC sizing
hedlok Offline
Junior Member
Registered: 03/25/06
Posts: 8
Loc: pa.
200A service with 4/0 alum. cond. what size GEC is okay? i know that table 250.66 says #4 but im in an arguement with someone who says it's not required to be any larger than #6. also, there is no rebar ground and plastic water service. what do you say?
Top
2017 / 2014 NEC & Related Books and Study Guides
#98541 - 05/31/06 07:43 PM Re: GEC sizing
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
250.66(A) says #6.
Top
#98542 - 05/31/06 08:35 PM Re: GEC sizing
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
A driven ground never needs more than #6 cu. Any other electrode, #4 cu.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 91 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals