#98501 - 12/30/04 05:52 PM Ground rod & water main
ToHo Offline
Member
Registered: 12/29/04
Posts: 46
Loc: N.Y.
Hi... Just wanted some feed back on installing 2 ground rods for a residential service instead of 1 ground rod and the water main. Speaking with a inspector here in Rochester NY , he said they would prefer to see 2 ground rods. That was new to me.. anybody have a opinion on this subject... thanks ToHo
Top
2017 / 2014 NEC & Related Books and Study Guides
#98502 - 12/30/04 06:20 PM Re: Ground rod & water main
CharlieE Offline
Member
Registered: 04/23/04
Posts: 204
Loc: Indianapolis
Please read 250.50. It requires the water piping system to be used as a grounding electrode (assuming it is in contact with the earth for 10 ft or more) and another grounding electrode. If the additional grounding electrode is a driven electrode, a maximum of 25 ohms must be met or a second one must be driven no closer than 6 ft to the first one.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#98503 - 12/30/04 06:59 PM Re: Ground rod & water main
ToHo Offline
Member
Registered: 12/29/04
Posts: 46
Loc: N.Y.
Thanks charlie... I agree 100%. Its always nice to get another view. If a well is used on the premise w/ pvc piping into the house. Would you use 2 ground rods or could you use only one if the ohms reading was acceptable?
Top
#98504 - 12/30/04 09:42 PM Re: Ground rod & water main
Gary S Offline
Member
Registered: 12/29/04
Posts: 12
Loc: Houston, Texas, USA
You would be compliant with only one rod as long as the resistance is less than 25 ohms. Also, even though the waterpipe from the well is PVC, if the water system in the house is metallic, then it must still be bonded to the service. Not as an electrode, but to make it the same potential as the equipment grounds.
Top
#98505 - 12/31/04 05:53 AM Re: Ground rod & water main
CharlieE Offline
Member
Registered: 04/23/04
Posts: 204
Loc: Indianapolis
Gary, I agree completely.
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 69 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals