The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 192 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#98495 - 12/20/04 07:29 AM Circuit Integrity (CI) Cable
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Does anyone have any experience with this cable?

Looking for all temperature ratings, and type of fires, etc?
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#98496 - 12/20/04 10:47 AM Re: Circuit Integrity (CI) Cable
therain4 Offline
Member

Registered: 12/18/00
Posts: 37
Loc: Dunmore,Pa. U>S.A.
Where is this cable in the 2005 Code? By the way I love the new page numbering system.

Top
#98497 - 12/20/04 10:54 AM Re: Circuit Integrity (CI) Cable
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
It's in just about all of the low voltage/limited energy articles, such as 725, 760, etc...
_________________________
Ryan Jackson,
Salt Lake City

Top
#98498 - 12/20/04 01:08 PM Re: Circuit Integrity (CI) Cable
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
It has been in the code at least one cycle already. I've specified it, and it seems to be ok. You can use CI cable for use with or without raceway, and CIC for use with raceway. The manufacturer that was low bid was http://www.vitalinkcable.com/
but there are others.
_________________________
Ron

Top
#98499 - 12/22/04 08:29 AM Re: Circuit Integrity (CI) Cable
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Thank you Ron, very helpful link!

I searched the 2002 NEC and found the following areas where Type CI is included, but did not look at the 2005 yet.. I think there may be more locations:

 Quote:
Fire Alarm Circuit Integrity (CI) Cable. Cable used in fire alarm systems to ensure continued operation of critical circuits during a specified time under fire conditions.

(F) Fire Alarm Circuit Integrity (CI) Cable. Cables suitable for use in fire alarm systems to ensure survivability of critical circuits during a specified time under fire conditions shall be listed as circuit integrity (CI) cable.

Cables identified in 760.31(C), (D), and (E) that meet the requirements for circuit integrity shall have the additional classification using the suffix “CI” (for example, NPLFP-CI, NPLFR-CI, and NPLF-CI).

FPN No. 2: One method of defining circuit integrity (CI) cable is by establishing a minimum 2-hour fire resistance rating for the cable when tested in accordance with UL 2196-1995, Standard for Tests of Fire Resistive Cables.

(G) Fire Alarm Circuit Integrity (CI) Cable. Cables suitable for use in fire alarm systems to ensure survivability of critical circuits during a specified time under fire conditions shall be listed as circuit integrity (CI) cable. Cables identified in 760.71(D), (E), and (F) that meet the requirements for circuit integrity shall have the additional classification using the suffix “CI” (for example, FPLP-CI, FPLR-CI, and FPL-CI).
_________________________
Joe Tedesco, NEC Consultant

Top
#98500 - 12/22/04 08:30 AM Re: Circuit Integrity (CI) Cable
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Thank you Ron, that's a very helpful link!

deleted duplicate

[This message has been edited by Joe Tedesco (edited 12-22-2004).]
_________________________
Joe Tedesco, NEC Consultant