#98470 - 10/24/04 03:18 PM Range hoods require an individual branch circuit  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Look at what is NEW in Article 422 for cord and plug connected Range Hoods!

.......

Quote
(5) The receptacle shall be supplied by an individual branch circuit.


[See ROP 17–21]

Why? What was the substantiation?


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#98471 - 10/24/04 03:26 PM Re: Range hoods require an individual branch circuit  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
That is a good question Joe.

Do you mind if I just guess at the substantiation?

Could it be that it is expected a microwave hood combo unit may be installed at some later date?

I hope I am wrong about that.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#98472 - 10/24/04 03:39 PM Re: Range hoods require an individual branch circuit  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Not making light of the issue, but I must live a sheltered life in that I have never installed a cord and plug connected range hood.

Roger


#98473 - 10/24/04 03:52 PM Re: Range hoods require an individual branch circuit  
capt al  Offline
Member
Joined: Jun 2004
Posts: 206
Norton, Ma USA
Roger, guess I have lived the same way. Never installed one in the 25 years I've been doing electrical work. Every range hood I have connected was hard wired.

Al


#98474 - 10/24/04 04:00 PM Re: Range hoods require an individual branch circuit  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Hello Al, whew, I'm glad I'm not alone here. [Linked Image]

Roger


#98475 - 10/24/04 04:04 PM Re: Range hoods require an individual branch circuit  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Roger and Al where did you locate the disconnect switch?

Not in the cabinet I hope, that would be a 110.26 violation. [Linked Image]

Just kidding I have only seen hard wired hoods also.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#98476 - 10/24/04 06:28 PM Re: Range hoods require an individual branch circuit  
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
One reason you guys may not have seen a cord connected range hood is that they are sold at the Big Box stores and usually not installed by 'electricians'.

422.16(B)(4)Range Hoods.
Range hoods shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for the use on range hoods in the installation instructions of the appliance manufacturer, where all of the following conditions are met:


Bob, your reasoning is right on the money! See page 206 of the 2005 Analysis book.


Substantiation:
Many times range hoods are removed and replaced with a "microwave type" range hood. Allowing cord and plug connection will make the installation much easier for the homeowner because no "electrical change" to the wiring system will be required.

Panel Statement:
The permission to use cord-and-plug connection provides the ability to upgrade to a combined microwave range hood. The panel added the additional requirements to ensure a safe installation of a combined microwave range hood.


***This statement and code change says something to me that makes me very uneasy. Why is the NEC making code changes based on Homeowners performing installations. ELECTRICIANS should be installing electrical work and using the NEC as well as their learned skills from the field.****

Pierre


Pierre Belarge

#98477 - 10/24/04 06:37 PM Re: Range hoods require an individual branch circuit  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I agree Pierre. It sure seems strange that this passed. How many proposals do you see that really are good ideas but have no technical substantiation and get shot down because of it? It seems to me that this is no diffferent than the rest of them.


Ryan Jackson,
Salt Lake City

#98478 - 10/24/04 06:51 PM Re: Range hoods require an individual branch circuit  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Pierre

Quote
This statement and code change says something to me that makes me very uneasy. Why is the NEC making code changes based on Homeowners performing installations. ELECTRICIANS should be installing electrical work and using the NEC as well as their learned skills from the field


Well said.

I also think of this.

Quote
This Code contains provisions that are considered necessary for safety. Compliance therewith and proper maintenance will result in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use.


With this reasoning 30 and 50 amp outlets should be provided at gas dryers and ranges in case the homeowner decides to change to electric in the future.

We better run 10/3 to this hood outlet in case the microwave hood combo that might be installed has browning elements.

Well I can't complain as I was not involved in the code making process. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#98479 - 10/24/04 07:54 PM Re: Range hoods require an individual branch circuit  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
I have been giving residential hoods thier own circuit for years. Most of the higher end ones really suck if you know what I mean, multiple motors, lighting, heat lamps, etc. Some will pull upwards of 12A. Justification alone for a dedicated circuit. However, I haven't seen one cord connected yet either??? Where would one place a plug for such an animale?


Mark Heller
"Well - I oughta....." -Jackie Gleason

Page 1 of 3 1 2 3

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.003s) Memory: 0.8193 MB (Peak: 0.9953 MB) Zlib enabled. Server Time: 2017-03-25 00:02:45 UTC