The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
Today at 09:09 PM
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 139 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#98434 - 02/20/05 04:45 PM Mass revision 334.80
shortcircuit Offline

Registered: 06/27/04
Posts: 608
Loc: massachusetts
334.80 says type NM (romex) shall have conductors rated 90 degrees C

So...the romex used in the 80's had conductors rated 60 degrees C

So... in this kitchen remodel I'm doing (the one we already determined that I have to replace the type SE range line), can I use the old branch circuit romex feeding the kitchen, which has conductors rated 60 degrees C, bring them into a juction box and extend new 90 degree C romex to the new plug locations, dishwasher, micro, etc???

The panel is located in a plastered garage and it will be difficult to access.

Or would Mass Rule 3 apply here also?


2014 / 2011 NEC & Related Books and Study Guides
#98435 - 02/21/05 05:56 AM Re: Mass revision 334.80
Electricmanscott Offline

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
I think you would be ok. I have done this many times and the only time it was ever questioned the inspector wanted to make sure the old wire did not connect directly to a light fixture.