The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 102 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#98373 - 10/26/04 07:52 PM GFCI changes
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Residential change:

Item (7) revised to read:
 Quote:
Laundry, utility, and wet bar sinks-where the receptacles are installed within 6' of the outside edge of the sink.



Commercial changes: Items (2) which was previously item (3) revised to read:
 Quote:
Commercial and institutional kitchens-for the purpose of this section, a kitchen is an area with a sink and permanant facilities for food preperation and cooking.


New item (4) reads:
 Quote:
Outdoors in public spaces-for the purpose of this section a public space is defined as any space that is for use by, or is accessible to, the public


New item (5) reads:
 Quote:
Outdoors, where installed to comply with 210.63


So, regarding the residential change, two things come to my mind...
1: What about the washing machine in the laundry that is within 6' of the sink, and
2: The 2002 addressed the countertop receptacles for wet bar sinks. Now it just says within 6'. What about a cord and plug connected garbage disposal under the sink?

[This message has been edited by Ryan_J (edited 10-27-2004).]
_________________________
Ryan Jackson,
Salt Lake City

Top
2014 / 2011 NEC & Related Books and Study Guides
#98374 - 10/27/04 09:52 AM Re: GFCI changes
ElectricAL Offline
Member

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
Ryan,

Great question.
 Quote:
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.

(A) Dwelling Units.
All 125-volt single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.
.
.
.

(7) Laundry, utility, and wet bar sinks -- where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink


If my laundry equipment is plugged into a receptacle within 6' of the utility sink, then it seems that the machines must be GFIed. There are no exceptions related to (7) that I could find.
_________________________
Al Hildenbrand

Top
#98375 - 10/27/04 10:18 AM Re: GFCI changes
ElectricAL Offline
Member

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
I'm sitting here still thinking about this. . .

It seems that the requirement becomes a volume of space that is covered by the GFI. That is, a sink "GFI zone", for a sink mounted in a 3' high counter, will include an area of the 8' high ceiling above the sink, as well as the clock outlet on the wall above the sink.

And, if the sink is mounted against a "half wall" partition separating a single area into a kitchen and eating area, the receptacles within 6' on the eating area side of the partition should also be GFIed.
_________________________
Al Hildenbrand

Top
#98376 - 10/27/04 03:13 PM Re: GFCI changes
ElectricAL Offline
Member

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
And I can think of a lot of small kitchen layouts that, based on how I read this, will now be required to have GFI protection on the refir and gas range receptacles.
_________________________
Al Hildenbrand

Top
#98377 - 10/27/04 03:17 PM Re: GFCI changes
ElectricAL Offline
Member

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
Is a kitchen sink a wet bar sink?
_________________________
Al Hildenbrand

Top
#98378 - 10/27/04 03:31 PM Re: GFCI changes
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
No, but I'm not sure what a kitchen is anymore :-P

I would say no, since they each have their own seperate GFCI provisions in 210.8(A). Kitchens require the counter receptacles, wet bars require all within 6'...

Although....there is a mistake in the 2005 that defines kitchen for 210.8(A). It is found it 210.8(B)(2), which says for the purpose of this section, a kitchen is.... According to the NEC style manual, this definition applies to everything in 210.8, since that is the code section. 210.8(B)(2) is a subsection. So, in my opinion, a residential kitchen is an area with a sink and permanant facilities for food preperation and cooking.
_________________________
Ryan Jackson,
Salt Lake City

Top
#98379 - 10/28/04 06:59 PM Re: GFCI changes
John Steinke Offline
Member

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
Perhaps we can compare this to GFCI rules for garages- where an exception exists for dedicated receptacles (such as for a refrigerator or freezer).

Top
#98380 - 10/28/04 07:24 PM Re: GFCI changes
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
John...I wouldn't allow it. There is no exception for this, and until there is I can't allow an alternate method, because 90.4 says that there must be equal protection for an altarnate. There is no equal to GFCI, in my opinion.
_________________________
Ryan Jackson,
Salt Lake City

Top
#98381 - 10/29/04 08:00 AM Re: GFCI changes
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
hi,
I did not think dedicated equipment like a washing machine or freezer has to be gfi protected?

-regards

Mustang
_________________________
Electricity has no respect for ignorance!

Top
#98382 - 10/29/04 09:33 AM Re: GFCI changes
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Mustang: There are no exceptions to this rule.
_________________________
Ryan Jackson,
Salt Lake City

Top
Page 1 of 3 1 2 3 >



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals