#98355 - 04/21/06 05:55 AM Dwelling unit service or feeder calculation
mweaver Offline
Junior Member
Registered: 11/16/04
Posts: 6
Loc: Salina Ks, 67401
I am having confusion regarding the proper calculation of a storage-type (120 gal or less) water heater within a dwelling calculation acomplished by the general method of calculaiton in the 2005 NEC.

By the general method, it is permissible to apply a demand of 75% when four or more dwelling unit appliances become part of the dwelling service or feeder calculation (Article 220.53). This I understand and with four or more appliances the 120 gal or less storage-type water heater would be subject to the demand. but ...

New to the 2005 NEC, A water heater is a continuous load (Article 422.13) .

The continuous load requirements for a feeder or service dictate that the portion of the feeder or service be sized 125% of any continuous load connected to the service or feeder (Articles 215.2(A)(1) for feeders and 230.42(A) for services.

With this in mind, would a storage-type water heater be: water heater load X 125% = water heater contonuous load X 75% for four or more appliances?



[This message has been edited by mweaver (edited 04-21-2006).]
Top
2017 / 2014 NEC & Related Books and Study Guides

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals