The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#98171 - 05/11/06 05:48 AM To bush or not to bush PVC
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Hey guys whats everyone`s interp of 352.46 then refer to 300.4f Here`s the deal wired mobil home pvc male adapter sch 80 pvc well I failed because no bushings on the pvc male adapters.Are they required in this situation? Using 4/0 quad cable direct burial. Thanks waiting for inspector to call us now as he left no reference yesterday.

Top
2014 / 2011 NEC & Related Books and Study Guides
#98172 - 05/11/06 06:05 AM Re: To bush or not to bush PVC
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
PVC may be non-conductive, but its edges are still sharp enough to damage insulation.
I think that's the reason behind 300.5H.
BTW, I always call for metallic elbows in underground PVC runs because the rope that pulls in the conductors can grind an edge in a PVC elbow during a tough pull. I've had cables fail to each other on an U/G feeder for just that reason before I adopted that little trick.
_________________________
Ghost307

Top
#98173 - 05/11/06 07:45 AM Re: To bush or not to bush PVC
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Hey no rope here. Dug 10 ft ditch sch 80 down from box to proper depth direct burial cables to other end pvc to box slide wires in. But pvc fittings are beveled smooth and I don`t see how they can damage the wiring.

Top
#98174 - 05/11/06 11:31 AM Re: To bush or not to bush PVC
giddonah Offline
Member

Registered: 06/03/05
Posts: 50
Loc: UT
Did he tell you exactly what point he was concerned with? Yes, the fittings are smooth, but when you cut a piece to length, the end isn't so smooth. Is there a point where wires exit through such an opening?

Top
#98175 - 05/11/06 11:38 AM Re: To bush or not to bush PVC
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You might be able to make a case that the burred end of a PVC pipe you cut with a chain saw could damage conductors but if this is the threaded end of a PVC male adapter, I don't see the issue. They are as smooth as the edges of a plastic bushing.
Both are mass produced injection molded plastic. The chance of a flaw in the process that leaves a rough edge is about the same for either.
_________________________
Greg Fretwell

Top
#98176 - 05/11/06 12:33 PM Re: To bush or not to bush PVC
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I am very doubtful that a PVC male adaptor provides a "smoothly rounded insulated surface" as discribed in 300.4(F) and would red tag the job without even hesitating. I'm comparing it to a female adaptor with a chase nipple or a threaded hub or boss that is an integral part of an enclousure. Sorry gentlemen.
_________________________
George Little

Top
#98177 - 05/11/06 02:16 PM Re: To bush or not to bush PVC
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
OK "the code" has spoken, (we should fail it)now has anyone actually seen a conductor damaged by a PVC fitting?
_________________________
Greg Fretwell

Top
#98178 - 05/11/06 03:42 PM Re: To bush or not to bush PVC
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
I hate to step in this one,,,


unforetally yes i did see few conductors got damaged by male termal adpator espcally after hard pull i did nick few of them [ugh !! ]

but the code required the bushing on the male adpator it been like that way for pretty long time i was not sure when it was enforeced.

I think it was debated before related with mobile home service hook up and kinda pretty common to get red flagged from this one if not carefull with bushing

Merci, Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#98179 - 05/11/06 03:48 PM Re: To bush or not to bush PVC
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
 Quote:
352.46 Bushings
Where a conduit enters a box, fitting, or other enclosure, a bushing or adapter shall be provided to protect the wire from abrasion unless the box, fitting, or enclosure design provides equivalent protection.

I think that a male adapter requires a bushing based on this section.
Don
_________________________
Don(resqcapt19)

Top
#98180 - 05/11/06 08:05 PM Re: To bush or not to bush PVC
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I looked at a few fittings and I agree. For some reason makes the edge sharper than it has to be, perhaps to sell more bushings. It would be quite easy to make the edge rounded to provide "equivilent protection"
_________________________
Greg Fretwell

Top