The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 230 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 5 1 2 3 4 5 >
Topic Options
Rate This Topic
#98066 - 05/03/06 10:11 AM Multiwire circuit neutrals
kyelectric Offline
Member

Registered: 08/30/05
Posts: 64
Lets say you run 12/4 w/ground and use 3 as hots, 1 as neutral and 1 as ground. The three hots all go to 20 amp breakers. Two of the three circuits will feed out to my kitchen countertop required small appliance branch circuits (GFI protected). The other circuit will be a dedicated receptacle for a plug and cord garbage disposal. At what point do I know that I am overloading the neutral? What are the rules about how many circuits you can run off of one neutral? Any help would be appreciated.

Top
2014 / 2011 NEC & Related Books and Study Guides
#98067 - 05/03/06 10:14 AM Re: Multiwire circuit neutrals
macmikeman Offline
Member

Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
What is the system voltage in this kitchen you are refering to?

Top
#98068 - 05/03/06 11:16 AM Re: Multiwire circuit neutrals
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
If this is not 3 legs of a 3p wye it is a violation and you will be overloading the neutral.

Art 100 definition of multiwire;
Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
_________________________
Greg Fretwell

Top
#98069 - 05/03/06 11:49 AM Re: Multiwire circuit neutrals
dlhoule Offline
Member

Registered: 04/28/05
Posts: 71
Loc: Saline, MI 48197
If this is not 3 legs of a 3p wye it is a violation and you will be overloading the neutral.
Art 100 definition of multiwire;
Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.

Perhaps I'm just dense, but how does that definition make it illegal if it is not 3 legs of a wye. If you used a #10 gc and 3 #14s from any 240 V source; IMO it would be legal and satisfy the NEC.

Top
#98070 - 05/03/06 01:03 PM Re: Multiwire circuit neutrals
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Dlhoule, in your example it would be legal. The #10 would carry the maximum amperage of the two # 14 ungrounded conductors on the same leg.

Roger

Top
#98071 - 05/03/06 02:30 PM Re: Multiwire circuit neutrals
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I don't agree with the example of using a #10 and 3 #14's for a few reasons:

1. Each ungrounded conductor must be a different color- which is not clearified in the example.
2. If it is a multi-wire branch circuit by virture of the fact that it is using 2 ungrounded conductiors that have a voltage between them per the definition, then I would not approve the additional ungrounded conductor tagging along on the grounded conductor of the multiwire branch circuit.
3. I am assuming that "#10 gc" means grounded conductor.
4. 210.4 (C) makes it to debateable and on top of that ir's wierd.
_________________________
George Little

Top
#98072 - 05/03/06 02:43 PM Re: Multiwire circuit neutrals
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
George than I have to ask if you think this is a case where the handbook is wrong?


Exhibit 225.3 A 120/240-volt, single-phase, 3-wire system (branch circuits rated at 20 amperes; maximum unbalanced current of 80 amperes).

Bob

[This message has been edited by iwire (edited 05-03-2006).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#98073 - 05/03/06 03:26 PM Re: Multiwire circuit neutrals
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
The diagram posted by Iwire comes from Article 225- Outside Branch Circuits and Feeders and is permitted outdoors (225.7(B)), but would not be permitted indoors as far as I can tell since there is no similar language in Article 210 Branch Circuits.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#98074 - 05/03/06 03:47 PM Re: Multiwire circuit neutrals
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
True Tom, but where is the language that prevents it?

What code section can be cited to fail it and why should there be one.

It is as safe as a feeder.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#98075 - 05/03/06 03:48 PM Re: Multiwire circuit neutrals
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
You are correct Bob. That is a good example. When I made that post I somehow knew you'd bring that up. I still say it's a poor design and an installer who installs this way is just asking for trouble. I can't give him a violation but I can first of all try and talk him out of it due to the potential for confusinon down the road and if that don't work you can bet your beppi he will be submitting an asbuilt showing all the intimate details of the cicuiting, wire numbering, loading and not just a skimpy sketch on piece of scratch paper either.

I have never seen anyone install anything even remotely close to that in real life. I've been in the trad for 40 years and an inspector for over 20.

I take that back- I did have a guy one time install some festoon lighting where he had a common neutral.