#98041 - 04/29/06 02:36 PM De-icing & snow melting equip
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Does anyone on this BB have any experience with mats installed in concrete driveways for snow melting or de-icing? I have a contractor that says that when you have mulitple mats, the manufacturer specs tell him to splice the leads in a "T" conduit body and it is acceptable to bury said conduit body in the concrete??? I've asked him for info from the manufacturer. This splice would be not accessible. Need your comments before Monday.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#98042 - 04/29/06 03:17 PM Re: De-icing & snow melting equip
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
Sounds crazy to me George.

I don't have any experience to relate to your situation but I would think that would be a last ditch option.

How long are the leads on the mats?

GJ
Top
#98043 - 04/29/06 05:11 PM Re: De-icing & snow melting equip
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Since any repair would require busting up the concrete anyway I am not sure of why there would be a problem with this approach.
I suppose they could expose the cover of the conduit body but I am not sure what that accomplishes beyond creating a more likely place to fail.
_________________________
Greg Fretwell
Top
#98044 - 04/30/06 07:28 AM Re: De-icing & snow melting equip
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
George,
check 426.22 (NEC2002) The type of leads makes a diference about needing conduit or not. Splices with a direct burial coating would IMHO be accepted.
The buried conduit could be a Code violation if you look at 426.3
Also check 426.24 B and the reference to 300.15

Most installers are not aware of the requirement of 426.13. A warning sign must be posted to keep some contractor from cutting the concrete when the heat is turned on.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkync), 67 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals