The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 208 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#98041 - 04/29/06 02:36 PM De-icing & snow melting equip
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Does anyone on this BB have any experience with mats installed in concrete driveways for snow melting or de-icing? I have a contractor that says that when you have mulitple mats, the manufacturer specs tell him to splice the leads in a "T" conduit body and it is acceptable to bury said conduit body in the concrete??? I've asked him for info from the manufacturer. This splice would be not accessible. Need your comments before Monday.
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#98042 - 04/29/06 03:17 PM Re: De-icing & snow melting equip
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
Sounds crazy to me George.

I don't have any experience to relate to your situation but I would think that would be a last ditch option.

How long are the leads on the mats?

GJ

Top
#98043 - 04/29/06 05:11 PM Re: De-icing & snow melting equip
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Since any repair would require busting up the concrete anyway I am not sure of why there would be a problem with this approach.
I suppose they could expose the cover of the conduit body but I am not sure what that accomplishes beyond creating a more likely place to fail.
_________________________
Greg Fretwell

Top
#98044 - 04/30/06 07:28 AM Re: De-icing & snow melting equip
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
George,
check 426.22 (NEC2002) The type of leads makes a diference about needing conduit or not. Splices with a direct burial coating would IMHO be accepted.
The buried conduit could be a Code violation if you look at 426.3
Also check 426.24 B and the reference to 300.15

Most installers are not aware of the requirement of 426.13. A warning sign must be posted to keep some contractor from cutting the concrete when the heat is turned on.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.

Top