The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 255 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97959 - 04/19/06 03:09 AM Air Compressor Nameplate
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
Re: Sizing overcurrent protective devices, disconnects and wire. 5 HP 230 volts, single phase bolted to the floor air compressor. The nameplate amps = 23. Using the proper table in article 430, amps = 28. My question is: Is the air compressor considered an appliance thus should article 422 be used? I used to always use the amps listed in the tables in article 430. However, I believe the air compressor could be considered an appliance and the nameplate amps could be used.

Top
2014 / 2011 NEC & Related Books and Study Guides
#97960 - 04/19/06 06:56 AM Re: Air Compressor Nameplate
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Frank,

Yes it is an appliance, but, look at 422.3:
"The requirements of Article 430 shall apply the the installation of motor-operated appliances..."
and 422.12(G): "Motors of motor-operated appliances shall be provided with overload protection in accordance with Part III of Article 430."
We use the nameplate for the overload (heaters) protection, and the tables from Article 430 for the short circuit and ground fault protection, and choosing the size of the conductors and disconnects.
_________________________
Earl

Top