The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#97857 - 04/05/06 06:47 PM min ampacity of feeder for sub panel 4 ckts
gserve Offline
Member
Registered: 03/11/03
Posts: 92
On a sub panel installation in a residential garage of 4 two wire branch circuits I say that the min feeder ampacity should be 60A. Based on the fact that the disconnecting means must be rated at 60 A by code. My co-worker says that it is based on the computed load and could be 40A or 50A. Please advise with code reference. Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#97858 - 04/05/06 08:07 PM Re: min ampacity of feeder for sub panel 4 ckts
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I would be more interested in a reference for the idea that a feeder to a sub panel has to be 60a.
It would not have to be any more than the computed load as far as I know and that may easily be less than the combined breaker handle amps in the sub panel.

... but I amy owe someone an appology.
_________________________
Greg Fretwell
Top
#97859 - 04/05/06 11:17 PM Re: min ampacity of feeder for sub panel 4 ckts
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I was just over at Joe's house and I saw Mike's answer to you. Are we talking about the ampacity of the feeder or the rating of the garage disconnect?
_________________________
Greg Fretwell
Top
#97860 - 04/06/06 06:30 AM Re: min ampacity of feeder for sub panel 4 ckts
luckyshadow Offline
Member
Registered: 01/04/05
Posts: 305
Loc: Maryland USA
In the '05 NEC - 225.39 (D)
I think this is what everyone is referring to.
Top
#97861 - 04/06/06 07:08 AM Re: min ampacity of feeder for sub panel 4 ckts
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
That only refers to the interrupting rating of the disconnect, not the ampacity of the feeder.
_________________________
Greg Fretwell
Top
#97862 - 04/07/06 05:38 AM Re: min ampacity of feeder for sub panel 4 ckts
luckyshadow Offline
Member
Registered: 01/04/05
Posts: 305
Loc: Maryland USA
225.39 The feeder or branch-circuit disconnecting means shall have a rating not less than the load to be supplied, determined in accordance with parts 1 and 2 of article 220 for branch circuits, parts 3 or 4 of article 220 for feeders, or part 5 of article 220 for farm loads. In no case shall the rating be lower then specified in 225.39 (A)(B)(C)(D).
(A) - One circuit Installation - does not apply to this thread
(B) - two circuit Installation - Does not apply to this thread
(C) - One Family Dwelling _ Does not apply to this thread
(D) - ALL OTHERS. For all other installations( this is us) the FEEDER or branch-circuit Disconnecting means shall have a rating of NOT less than 60 amperes.

I read this as saying that the FEEDER must be at least 60 amperes because it states the FEEDER or branch-circuit DISCONNECTING means ....
Isn't the the circuit breaker in the main panel the DISCONNECTING MEANS for this FEEDER ?
Top
#97863 - 04/07/06 10:01 AM Re: min ampacity of feeder for sub panel 4 ckts
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
You have to read the NEC in context. You don't simply cherry pick words out of context.
This section is titled "More than one building or other structure" and 225.39 is titled "rating of disconnect" (in that other building) so it does not refer to the breaker in the main building (see "location" in 225.32) or the ampacity of the feeder, only the disconnect in the "other" building. They just want to insure that you can safely disconnect the "other" building, under load, at that building if you need to.

[This message has been edited by gfretwell (edited 04-07-2006).]
_________________________
Greg Fretwell
Top
#97864 - 04/07/06 11:06 AM Re: min ampacity of feeder for sub panel 4 ckts
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
One could also be using a 60a. fuse type disconnect and install smaller wires and fuses in said disconnect at the house.
_________________________
George Little
Top
#97865 - 04/07/06 08:34 PM Re: min ampacity of feeder for sub panel 4 ckts
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
George, I suppose I would have to hold my nose and approve one of those 60 a "pull out only" disconnects you see in HVAC units but I don't think I would actually want to pull one under load without PPE.
_________________________
Greg Fretwell
Top
#97866 - 04/08/06 09:44 AM Re: min ampacity of feeder for sub panel 4 ckts
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Yeah, Greg, I'd agree with you on the "hold my nose". I've been an inspector for 20 years and a contractor prior to that for 12 years. One of the toughest things I had to adjust to was that everyone has a different level of professionalism and some of them are not at the same level as I am but they still meet minimum code. Of course there are those who are really perfectionist and they exceed code by a wide margin making the inspectors job easier.
_________________________
George Little
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
2 registered (Admin, HotLine1), 103 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals