The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97806 - 03/28/06 01:46 PM Fire Alarm Wiring
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Based on the 2002 NFPA72, is it now permissible to have the outgoing and return conductors in the same bridle rings when installing a Class A fire alarm circuit??

[This message has been edited by George Little (edited 03-28-2006).]
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#97807 - 03/28/06 02:31 PM Re: Fire Alarm Wiring
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Generally yes, same bridle ring, different cable, unless specified by Contract differently.

6.4.2.2.2 All styles of Class A circuits using physical conductors (e.g., metallic, optical fiber) shall be installed such that the outgoing and return conductors, exiting from and returning to the control unit, respectively, are routed separately. The outgoing and return (redundant) circuit conductors shall not be run in the same cable assembly (i.e., multi-conductor cable), enclosure, or raceway.

Exception: The outgoing and return (redundant) circuit conductors shall be permitted to be run in the same cable assembly, enclosure, or raceway under any of the following conditions:
(1) For a distance not to exceed 3 m (10 ft) where the outgoing and return conductors enter or exit the initiating device, notification appliance, or control unit enclosures.
(2) Single conduit/raceway drops to individual devices or appliances.
(3) Single conduit/raceway drops to multiple devices or appliances installed within a single room not exceeding 92.9 m2 (1000 ft2) in area.

[This message has been edited by Ron (edited 03-28-2006).]

[This message has been edited by Ron (edited 03-28-2006).]
_________________________
Ron

Top
#97808 - 03/28/06 07:26 PM Re: Fire Alarm Wiring
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
What happened to the required spacing (recommended) called out in the appendix?
_________________________
George Little

Top
#97809 - 03/30/06 08:02 PM Re: Fire Alarm Wiring
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
The annex text is still there, but Annex A is not a part of the requirements of the NFPA document but is included for informational purposes only.

A.6.4.2.2.2
A goal of 6.4.2.2.2 is to provide adequate separation between the outgoing and return cables. This separation is required to help ensure protection of the cables from physical damage. The recommended minimum separation to prevent physical damage is 305 mm (1 ft) where the cable is installed vertically and 1.22 m (4 ft) where the cable is installed horizontally.



[This message has been edited by Ron (edited 03-30-2006).]
_________________________
Ron

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals