The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
Today at 01:42 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (Webmaster, LongRunner), 227 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97795 - 03/21/06 02:21 PM even more derating fun
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Section 310.15(B)(20(a) requires derating of more than 3 current carrying conductors in a cable or raceway.
Section 240.4(B) allows the next higher standard overcurrent device rating above the ampacity of the conductors being protected to be used.
Does that mean I can bundle 40 14/2 NM cables together for long distances, and connect each to a 15 amp cb?
80 current carrying conductors would require a 35% derating from 25 amps to 8.75 amps. Can I then bump the cb up to 15 amps because Section 240.6 gives me the lowest standard rated breaker as 15 amps?
Or, am I required to use a 10 amp fuse?
_________________________
Earl

Top
2014 / 2011 NEC & Related Books and Study Guides
#97796 - 03/21/06 02:28 PM Re: even more derating fun
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
IMO you could use the next standard size listed (15 amp) on any of the circuits that are not multioutlet branch circuits supplying receptacles for cord-and-plug-connected portable loads.

Of course the ampacity of the cables would still be only 8.75 amps and the connected load could not exceed that.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#97797 - 03/21/06 02:57 PM Re: even more derating fun
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
So, if we combine my two posts, using luminaires that do not draw more than 2 amps, I could get away with that scenenario?

12 current carrying conductors require a deration of 50%, 50% of 25 aamps is 12.5 amps. Dividing by six luminaires, gives me 2.08333 amps each.
_________________________
Earl

Top
#97798 - 03/21/06 03:15 PM Re: even more derating fun
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Cool questions.

IMO yes, 240.4(B) applies to the circuit as conditions (1), (2) and (3) are met and it tells us clearly "The next higher standard overcurrent device rating" a couple of times.

240.6 Standard Ampere Ratings shows the smallest standard rating as 15.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#97799 - 03/21/06 03:47 PM Re: even more derating fun
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I'm giving you guys a red sticker. Wording in the code is the "next higher standard overcurrent device" Not the next size circuit breaker. 10a. is the next size overcurrent device for earlydean's post. Guess someone is installing fuses on these circuits.
_________________________
George Little

Top
#97800 - 03/21/06 04:27 PM Re: even more derating fun
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I think that sticker should be pink instead of red, thereby giving partial credit. After all, Iwire did point out that going up to the next OCPD does not allow you to increase the ampacity (or load) of the conductors and he did correctly make the call about multioutlet circuits. These points seem to be lost on many, at least here in the Mountain State.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#97801 - 03/21/06 04:44 PM Re: even more derating fun
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Interesting, I have to agree with you George, that is what it says.

That aside I am not convinced the NEC intends to force the use of a fuse over a breaker.

Bob

BTW I will happily take a RED tag over a pink tag.

Pink is the color of the spare hardhats for those that always misplace their own.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#97802 - 03/25/06 08:09 AM Re: even more derating fun
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
It takes a real manly man to wear a pink hardhat on a construction job!
_________________________
Earl

Top