Joined: Mar 2003
Posts: 10
T
Member
517.80 of the NEC states:

Equivalent insulation and isolation to that required for the electrical distribution systems in patient care areas shall be provided for communications, signaling systems, data system circuits, fire alarm systems, and systems less than 120 volts, nominal.

FPN: An acceptable alternate means of providing isolation for patient/nurse call systems is by the use of nonelectrified signaling, communications, or control.

Would this mean all low voltage in a accessible drop ceiling located over a patient care area would need to be in EMT or FMC? And by insulation do they mean a literal interpretation ie; THHN THWN?

Any input would be appreciated, thanks

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,930
Likes: 34
G
Member
The short answer is yes.
There may be some mitigating factor somewhere but I always saw THHN in pipe for nurse calls and such.


Greg Fretwell