The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (geoff in UK), 133 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#97621 - 03/08/06 05:35 PM Device Removal
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
We had a brief discussion in my alternating current principles class last night. The instructor was convinced that all grounded conductors at a receptacle location had to be pigtailed in order to not break the grounded path. Obviously, that's the best way to do the wiring at the receptacles, but is it necessary by the NEC? I only see this rule applying to multiwire installations where breaking the neutral could do serious damage to an appliance (like a PLASMA TELEVISION) if ever broken.

Comments?

Top
2014 / 2011 NEC & Related Books and Study Guides
#97622 - 03/08/06 06:15 PM Re: Device Removal
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
You are correct. The rule in 300.13(B) only applies to the grounded conductor of a multiwire branch circuit.
Don
_________________________
Don(resqcapt19)

Top
#97623 - 03/08/06 07:35 PM Re: Device Removal
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
hey shock,
how would you do it without a pigtail?
put "two" wires under one recepticle ground screw?
if so; where is the ul listing for this type of device?
we all agree that the ground is the most important conductor and a pig tail would be the only way.

h20

Top
#97624 - 03/08/06 07:43 PM Re: Device Removal
Tiger Offline
Member

Registered: 05/04/05
Posts: 714
Loc: Crystal Lake, IL USA
The grounded conductor is the white/neutral

Dave

Top
#97625 - 03/09/06 12:53 AM Re: Device Removal
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
opps "ed" not "ing"
my mistake....
then i agree, no pigtail required by nec.
not sure about damage to equipment since the "grounding" would still be there.
on a multiwire you open neut at homerun and you put 240 across the circuits and this is never good. although power tools run really fast for a little while yuk yuk.

h20

Top
#97626 - 03/13/06 01:30 AM Re: Device Removal
tmegger64 Offline
Junior Member

Registered: 03/12/06
Posts: 7
Loc: Naples Fl.
Good Morning

What about 250.148(B)?

Tom

Top
#97627 - 03/13/06 01:33 AM Re: Device Removal
tmegger64 Offline
Junior Member

Registered: 03/12/06
Posts: 7
Loc: Naples Fl.
opps same thing with grounded and grounding, got to wake up this am sorry

Tom

Top
#97628 - 03/13/06 06:04 AM Re: Device Removal
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
The reason a device-dependent neutral path matters on multi-wire circuits is that, when handle-tied breakers are not used, one circuit can be deenergized to be worked on, but another sharing the same neutral can still be hot, making the load side of an opened neutral connection hot.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#97629 - 03/14/06 05:42 AM Re: Device Removal
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Larry, and isn't it true that if the grounded splice comes apart, one leg of the multiwire branch circuit will carry a higher voltage than the other ungrounded conductor? I seem to recall seeing/ reading this in one of my trade books somewhere. Could you explain why this happens?

Top
#97630 - 03/14/06 06:15 AM Re: Device Removal
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
At the risk of insulting everyone's intelligence on this forum I explain it this way- If you have a multi-wire branch circuit consisting of two ungrounded conductors and one grounded conductor, the loads of each of the ungrounded conductors are using the single grounded conductor for a return to the transformer. Should the grounded conductor be interrupted and the is no return to the transformer via the grounded conductor then the return path is through the other ungrounded conductor and any load on that other ungrounded conductor path, This could and probably would create a problem if the total current flow exceeded the limit of one of the components in this new found path back to the transformer. Example a 10a. load on one ungrounded conductor and a 1a. load on the other conductor now become a total load of 11a. and the 1a. load (100w. bulb for instance) would not tolerate the flow of 11a. and the bulb would burn out.
_________________________
George Little

Top
Page 1 of 2 1 2 >



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals