The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 216 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97617 - 03/06/06 05:24 PM Industrial Luminaires
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
I have a few fluorescent STYLE 'L' lights to hang and I was going to wire them using 14-3 SJ cord. Upon further review of the job, and the wiring method, I'm not sure if I will compy with code.

The lights will hang on jackchain that'll be attached to joists above a suspended ceiling. I want to tie-wrap the cord to the jackchain and run it through the ceiling to the junction box so the job will look as neat as possible. Article 400.7 (2) says cords can be used for luminaires, but article 400.8 (3) forbids running cords through a suspended ceiling. What should I do?

[This message has been edited by ShockMe77 (edited 03-06-2006).]

Top
2014 / 2011 NEC & Related Books and Study Guides
#97618 - 03/06/06 05:31 PM Re: Industrial Luminaires
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Don't use a cord, use AC or MC.
_________________________
Earl

Top
#97619 - 03/08/06 12:17 AM Re: Industrial Luminaires
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
What looks neat and meets Code: mount a receptacle within a junction box in the soft lid.

CADDY and B-Line make supports for it. (512)

Then just plug the SOJ into the receptacle.

SO/ SOJ cannot go above the lid: not rated for the heat up there.

The run from the receptacle junction box to the branch circuit would normally be MC.

A seismic wire to sustain the j-box would also be in order.

Otherwise, go all of the way with MC/ Greenfield. It looks nasty going through the lid. But it costs less.

You choose.
_________________________
Tesla

Top
#97620 - 03/08/06 07:23 AM Re: Industrial Luminaires
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Thanks for the replies, guys. I am going to come down with 12-2 MC at each fixture and do whatever splicing necessary in the ceiling above. I was just curious as to why the cord couldn't be run through the drop-ceiling (heat), now I know why. Thanks.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals