The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 186 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97487 - 02/22/06 04:55 PM supplemental grounding electrode
gserve Offline
Member

Registered: 03/11/03
Posts: 92
1)When a ufer ground is installed is a supplemental electrode required? (2) If one is required do I need 2 rods and do they have to be 6' min away from each other and the foundation?(as this is used for an electrode)(3)Can the #4 grounding electrode conductor be run through bored holes in the 2x10's to the panel?

Top
2014 / 2011 NEC & Related Books and Study Guides
#97488 - 02/22/06 05:31 PM Re: supplemental grounding electrode
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I remember reading Mr. Ufer's reports on his grounding electrode. Under extremely adverse conditions, his method always performed far better than the 25 ohms code calls for. This was confirmed by Max Macomb, in his documentation that finally persuaded the code panels to accept the "Ufer ground."

If you're measuring over 25 ohms, I would suspect a problem with the measurement method.

But, there is no rule agains adding an electrode if you want to....but it needs to be six feet, or more, from the Ufer...which, in this case, means the entire slab. With a "Ufer," your slab is the electrode- not just that little copper wire!

While many measure the resistance of the ground by simply sticking their meter probe in the dirt....there has to be a reason for those pricey clamp-on meters, and other fancy equipment, used to measure grounding impedence.

Top
#97489 - 02/22/06 05:47 PM Re: supplemental grounding electrode
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
Gserve:
In NEW construction, where a footing/foundation is being installed...it is mandatory that a Ufer be installed.

With a Ufer, no supplemental electrodes are required. (You may if you choose; they must be bonded together)

Yes, you may route the GEC thru wood framing.

As to the 'spacing'; IF you install, 6' spacing, like Reno stated above.

PS: You also have to 'bond' the water piping, jump the meter, bond the H&C at the wtr htr, etc.

John
_________________________
John

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals