#97478 - 02/21/06 07:52 AM Sharing grounds
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
When running multiple circuits from a panel to a juction box then splitting circuits off from there. I only need one ground to the junc box (sized to the largest conductor) then tie the rest of the grounds to a ground bar or lug from there. I don't need indivdual grounds for each circuit, unless its a GFI circuit. Correct?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
2017 / 2014 NEC & Related Books and Study Guides
#97479 - 02/21/06 09:17 AM Re: Sharing grounds
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Are you talking about equipment grounding conductors? Then yes, you just need one, sized to the largest O/C device.
The GFCI question confused me.
_________________________
Greg Fretwell
Top
#97480 - 02/21/06 10:24 AM Re: Sharing grounds
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
I don't know what a "ground" is. Are you asking about the grounded conductor or the equipment grounding conductor?
Don
_________________________
Don(resqcapt19)
Top
#97481 - 02/21/06 12:14 PM Re: Sharing grounds
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
Yes, equipment ground conductor. Not the neutral.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#97482 - 02/22/06 10:43 AM Re: Sharing grounds
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
Quote:
Yes, equipment ground conductor. Not the neutral.
Then I'd say your original question gets a yes answer but I don't see how the circuit being GFCI protected has any bearing on the question of the Equipment Grounding Conductor. Since the EGC does not pass through the sensing mechanism of the GFCI having only the one would have no effect on the GFCIs performance.
--
Tom

"This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison

[This message has been edited by tdhorne (edited 02-22-2006).]
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
#97483 - 02/22/06 05:01 PM Re: Sharing grounds
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
Your right, I probably don't need a separate ground for the GFI either, (neutral yes) but not ground. I'll just run the 3 - #8's for the spa heat pump to the pool equipment area junction box and branch off for the pool pump and GFI ground from there. I could run the motor frame bond wire there also. Where do they usually run the motor bond wire?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#97484 - 02/22/06 06:52 PM Re: Sharing grounds
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The only place you need an insulated, unspliced EGC is to a pool underwater light J box.
_________________________
Greg Fretwell
Top
#97485 - 02/23/06 10:25 PM Re: Sharing grounds
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
"then tie the rest of the grounds
to a "ground bar or lug"

how about some big blue wire nuts?
i have seen grounding conductors split bolted b-4, is it legal or smart for that matter to put several under a split bolt?

h20
Top
#97486 - 02/24/06 04:53 AM Re: Sharing grounds
sponge Offline
Member
Registered: 02/11/03
Posts: 31
[quote}
i have seen grounding conductors split bolted b-4, is it legal or smart for that matter to put several under a split bolt?

h20

[/quote]
Nope. Split bolts are not listed for this use.
John
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals