The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 214 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 4 1 2 3 4 >
Topic Options
Rate This Topic
#97406 - 02/18/06 04:37 PM sub panel detached building
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
i have a sub 50 amp sub panel that i want to put in a detached maint/gar building.
to save money on wire i am going to run two #6's for the lines and one #8 for the neutral(derating the neut)along with a #10 ground. my question is does this sound code compliant, we derate neutrals for the service feeders and this is going to be a feeder so it seems very complicit to me.

am i on the right page? any codes that i am missing which would forbid this derating?
thanks guys,
h20

Top
2014 / 2011 NEC & Related Books and Study Guides
#97407 - 02/18/06 04:39 PM Re: sub panel detached building
watersparkfalls Offline
Member

Registered: 03/08/05
Posts: 210
Loc: Washington...Not DC
oh yea it is a metal building which i will bond the beam structure and will drive two ground rods down at the building too.

Top
#97408 - 02/18/06 05:13 PM Re: sub panel detached building
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
By not knowing what your load is, I can't tell you that you can or can't derate the neutral. Also, I would be interested in how you terminate the neutral and ground wires in the sub panel. Where do you connect the Grounding Electrode Conductor in the sub panel?
_________________________
George Little

Top
#97409 - 02/18/06 06:02 PM Re: sub panel detached building
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
There's no need to install ground rods if you run a separate equipment grounding (bonding) conductor (E.G.C.) to the detached garage.

See more about this topic here: http://electrical-contractor.net/ubb/Forum1/HTML/006874.html

Top
#97410 - 02/18/06 06:03 PM Re: sub panel detached building
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey

Top
#97411 - 02/18/06 06:12 PM Re: sub panel detached building
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Hold on. You must ALWAYS install a grounding electrode system for a detached building with more than a single multiwire branch circuit. It doesn't matter if your have three or four wires; with or without an equipment grounding conductor.
see 250.32
_________________________
Earl

Top
#97412 - 02/18/06 06:16 PM Re: sub panel detached building
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
The neutral may only be derated if there is sufficient straight 240 volt loads to warrant it.
see 220.22
_________________________
Earl

Top
#97413 - 02/18/06 07:52 PM Re: sub panel detached building
markp Offline
Member

Registered: 04/12/04
Posts: 60
Loc: Kent, WA, USA
If your neutral busses are specifically listed at 75C and you use 75C rated wire, then #8 copper is fine for a 50A feeder because that wire is still rated at 50 amps.
_________________________
Mark
Kent, WA

Top
#97414 - 02/18/06 10:34 PM Re: sub panel detached building
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
My bad.

Yes, a grounding electrode MUST be installed on any detached building.

Top
#97415 - 02/19/06 07:09 AM Re: sub panel detached building
Speedy Petey Offline
Member

Registered: 08/29/03
Posts: 175
Loc: Upstate, NY
 Quote:
Yes, a grounding electrode MUST be installed on any detached building.

...that is fed with a feeder.
If you only run a circuit no rod is needed.
See: 250.32
_________________________
Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

Top