The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97297 - 02/16/06 12:17 AM separate branch circuit for elevator pit lighting and receptacles
ih17dka8 Offline
Junior Member

Registered: 01/16/06
Posts: 8
Loc: Seoul, South Korea
NEC 620.24(A) says that "A separate branch circuit shall supply the hoistway pit lighting and receptacles. Required lighting shall not be connected to the load side of a ground-fault circuit interrupter."

In our office, three electrical engineers have the each differenct interpretations.
Those are following.

A)Elevator pit lighting circuit is independent. so don't connect to any other lightings installed at near space out of pit. Elevator pit receptacles circuit is likewise. In addition to that, don't connect also between pit lighting and receptacle.

B)Elevator pit lighting doesn't need dedicated circuit. It can be connected to any other lightings at near space out of pit. However it shall not be connected to receptacles in elevator pit. Receptacles in pit are likewise.

C)Elevator pit lighting and receptacles are included in one circuit. No other lighting and receptacles of outside of pit excluded for that pit circuit.

What do you think which one is right?
I'll expect your considerable insight. Would you enlighten me on this question? Thank you all for your sincere opinion in ahead.

Top
2014 / 2011 NEC & Related Books and Study Guides
#97298 - 02/16/06 05:36 AM Re: separate branch circuit for elevator pit lighting and receptacles
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
I vote C.

Top
#97299 - 02/16/06 06:06 AM Re: separate branch circuit for elevator pit lighting and receptacles
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
"A separate branch circuit shall supply the hoistway pit lighting and receptacles."

That means one circuit for both.

"Required lighting shall not be connected to the load side of a ground-fault circuit interrupter."

That means line-side connection is okay.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#97300 - 02/16/06 06:17 AM Re: separate branch circuit for elevator pit lighting and receptacles
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
C also. Just be sure that the light is on the line side of the GFCI receptacle that's in the pit.
If you've got a cord connected sump pump in the pit, do the same thing. The separate circuit that 620.24(A) calls for if for the pit light and the pit "convenience" GFCI receptacle.
_________________________
Ghost307

Top
#97301 - 02/18/06 08:24 AM Re: separate branch circuit for elevator pit lighting and receptacles
luckyshadow Offline
Member

Registered: 01/04/05
Posts: 305
Loc: Maryland USA
In Maryland the State Elevator Inspector requires that Nothing else be on the circuit with the pit light and pit receptacle
Pit receptacle must be GFI and the Light Must NOT be on the load side of gfi. They will allow you to have them on seperate circuits,but nothing else can be on those circuits. We just run 1 circuit for both.
Also the Machine room receptacle must be GFI and on its own circuit. They are very strict with the Elevator shaft and machine room here.

Top
#97302 - 02/19/06 07:38 PM Re: separate branch circuit for elevator pit lighting and receptacles
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
To pass the elevator inspector's test the answer is A....

Nothing else will fly.
_________________________