The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
1 registered (cableguy619), 212 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97217 - 02/02/06 05:45 PM Ground wire to rods
Trick440 Offline
Member

Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
Does the ground wire to the 2 ground rods have to be continuous without breaks? Or can I have it go to the first ground rod secured with an acorn, then install another acorn to jump to the other rod?

So the ground wire is 2 pieces but attached with the acorns.
_________________________
Shake n Bake

Top
2014 / 2011 NEC & Related Books and Study Guides
#97218 - 02/02/06 06:24 PM Re: Ground wire to rods
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
No, it does not need to be an uninterrupetd run from the panel to both ground rods...only to the first one. This is the "GEC"
The wire between the two rods is considered a supplimental GEC.

Top
#97219 - 02/02/06 07:00 PM Re: Ground wire to rods
Trick440 Offline
Member

Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
thank you
_________________________
Shake n Bake

Top
#97220 - 02/03/06 02:15 PM Re: Ground wire to rods
eprice Offline
Member

Registered: 08/07/03
Posts: 64
Loc: North Logan, Utah, USA
I agree that the GEC ends at the first ground rod and does not need to continue unspliced from that point. However, conductors between ground rods or other electrodes in the grounding electrode system are more acurately called bonding jumpers. See 250.53(C)

Top
#97221 - 02/03/06 05:33 PM Re: Ground wire to rods
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Thanks, eprice....feel free to correct me!

Top
#97222 - 02/07/06 07:48 AM Re: Ground wire to rods
eprice Offline
Member

Registered: 08/07/03
Posts: 64
Loc: North Logan, Utah, USA
Well, alright, I will, but its just that I so seldom find anything to disagree with in what you say

Top
#97223 - 02/08/06 02:09 PM Re: Ground wire to rods
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
You may also want to check with your power company, ours insists that it be one wire, continuous.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#97224 - 02/16/06 03:32 PM Re: Ground wire to rods
LK Offline

Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Tom,

Could you please send me a copy of that requirement for the continous run, is that Allegheny Power?

Thank you,

Les

[This message has been edited by LK (edited 02-16-2006).]