#97217 - 02/02/06 05:45 PM Ground wire to rods
Trick440 Offline
Member
Registered: 08/15/05
Posts: 247
Loc: Waterford, MI, USA
Does the ground wire to the 2 ground rods have to be continuous without breaks? Or can I have it go to the first ground rod secured with an acorn, then install another acorn to jump to the other rod?

So the ground wire is 2 pieces but attached with the acorns.
_________________________
Shake n Bake
Top
2017 / 2014 NEC & Related Books and Study Guides
#97218 - 02/02/06 06:24 PM Re: Ground wire to rods
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
No, it does not need to be an uninterrupetd run from the panel to both ground rods...only to the first one. This is the "GEC"
The wire between the two rods is considered a supplimental GEC.
Top
#97219 - 02/02/06 07:00 PM Re: Ground wire to rods
Trick440 Offline
Member
Registered: 08/15/05
Posts: 247
Loc: Waterford, MI, USA
thank you
_________________________
Shake n Bake
Top
#97220 - 02/03/06 02:15 PM Re: Ground wire to rods
eprice Offline
Member
Registered: 08/07/03
Posts: 64
Loc: North Logan, Utah, USA
I agree that the GEC ends at the first ground rod and does not need to continue unspliced from that point. However, conductors between ground rods or other electrodes in the grounding electrode system are more acurately called bonding jumpers. See 250.53(C)
Top
#97221 - 02/03/06 05:33 PM Re: Ground wire to rods
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Thanks, eprice....feel free to correct me!
Top
#97222 - 02/07/06 07:48 AM Re: Ground wire to rods
eprice Offline
Member
Registered: 08/07/03
Posts: 64
Loc: North Logan, Utah, USA
Well, alright, I will, but its just that I so seldom find anything to disagree with in what you say
Top
#97223 - 02/08/06 02:09 PM Re: Ground wire to rods
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
You may also want to check with your power company, ours insists that it be one wire, continuous.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#97224 - 02/16/06 03:32 PM Re: Ground wire to rods
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
Tom,

Could you please send me a copy of that requirement for the continous run, is that Allegheny Power?

Thank you,

Les

[This message has been edited by LK (edited 02-16-2006).]
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals