The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97194 - 01/31/06 08:27 PM Sizing conductors for 4gang meterbase
highground Offline
Member

Registered: 11/14/04
Posts: 50
Loc: Chama, NM
Installing a 4 gang meterbase to feed 4 dwellings not yet constructed. Service to be supplied by the developer. (100A mains in meterbase). How are the conductors feeding this meterbase to be sized? Total connected load?
Code reference?
Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#97195 - 01/31/06 09:55 PM Re: Sizing conductors for 4gang meterbase
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You really need a 220 load calc per 230.23(A).
Example D4(a) will give you an idea what it will look like.
_________________________