The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
21 minutes 40 seconds ago
Re: Fabricating Guards out of Lexan?
by frank
Today at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Today at 01:26 PM
Why cables look like they do
by Texas_Ranger
Today at 12:33 PM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 20
Webmaster 18
ghost307 12
gfretwell 12
Trumpy 12
Who's Online
1 registered (Webmaster), 0 Guests and 52 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97194 - 01/31/06 08:27 PM Sizing conductors for 4gang meterbase
highground Offline
Member

Registered: 11/14/04
Posts: 50
Loc: Chama, NM
Installing a 4 gang meterbase to feed 4 dwellings not yet constructed. Service to be supplied by the developer. (100A mains in meterbase). How are the conductors feeding this meterbase to be sized? Total connected load?
Code reference?
Thanks

Top
2017 / 2014 NEC & Related Books and Study Guides
#97195 - 01/31/06 09:55 PM Re: Sizing conductors for 4gang meterbase
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9061
Loc: Estero,Fl,usa
You really need a 220 load calc per 230.23(A).
Example D4(a) will give you an idea what it will look like.
_________________________