The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (sparkyinak), 205 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#97194 - 01/31/06 08:27 PM Sizing conductors for 4gang meterbase
highground Offline

Registered: 11/14/04
Posts: 50
Loc: Chama, NM
Installing a 4 gang meterbase to feed 4 dwellings not yet constructed. Service to be supplied by the developer. (100A mains in meterbase). How are the conductors feeding this meterbase to be sized? Total connected load?
Code reference?

2014 / 2011 NEC & Related Books and Study Guides
#97195 - 01/31/06 09:55 PM Re: Sizing conductors for 4gang meterbase
gfretwell Offline


Registered: 07/20/04
Posts: 9024
Loc: Estero,Fl,usa
You really need a 220 load calc per 230.23(A).
Example D4(a) will give you an idea what it will look like.