#97146 - 01/26/06 04:16 PM Lights & Receptacles
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Lighting outlets and receptacle outlets on the same branch circuit in a non-residential facility. Assuming adequate circuit capacity, is this a code, or design issue?

Thanks.
Top
2017 / 2014 NEC & Related Books and Study Guides
#97147 - 01/26/06 04:30 PM Re: Lights & Receptacles
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Design issue.

Prior to the use of EBU's in Michigan we kept the lights and receptacles separate.
_________________________
George Little
Top
#97148 - 01/26/06 04:31 PM Re: Lights & Receptacles
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
I believe the same 50% rule applies.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#97149 - 01/26/06 04:49 PM Re: Lights & Receptacles
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Thanks guys.
It must be one of those mysterious "hearsay code" rules.

Larry,

210.23(A)(2) would seem to specifically exclude fixtures from the 50% rule?
Top
#97150 - 01/27/06 05:51 AM Re: Lights & Receptacles
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
Then you have my blessings. There is still a concern that a malfunctioning equipment could leave one in the dark, but egress lighting should come into play.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#97151 - 01/28/06 07:52 AM Re: Lights & Receptacles
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Redsy:
Design issue...albeit a questionable design, can't put the NEC to blame. As Larry said, lighting issue may arise.

All in all, NOT on my comm job.

John
_________________________
John
Top
#97152 - 01/28/06 10:24 AM Re: Lights & Receptacles
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
To continue the discussion, I rarely combine lighting and receptacles even in residential work. It saves money, time, troubleshooting, and is better for the homeowner, who doesn't lose 100% of power in a room from a single fault.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#97153 - 01/28/06 10:40 AM Re: Lights & Receptacles
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Suppling the 120 volt receptacles from the 277 volt lighting circuits raises heck with PCs and power tools.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#97154 - 01/28/06 02:45 PM Re: Lights & Receptacles
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
Yeah, but if you're in a hurry, it's great for a few minutes.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#97155 - 01/28/06 04:17 PM Re: Lights & Receptacles
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Thanks guys!
There were several time in my old facility when miss secretary plugged in a ceramic heater to warm her toes and left others "in the dark".
This case invloves pulling a new surface run off an existing flush receptacle, in order to eliminate an extension cord (no additional load expected). But, as it turns out the receptacle is fed from the light switch in the storage room behind it. I'm not yet sure if any other lights(or receptacles)are on the circuit.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals