#97141 - 01/25/06 01:46 PM emergency electric rm.
jmcelectric Offline
Member
Registered: 01/20/04
Posts: 16
Is it ok to run a 4" feeder for a 400a normal power panel through an emergency electric room,or do i need a 2hr seperation? I can't find it anywhere in the code that says i can't.Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#97142 - 01/29/06 05:46 PM Re: emergency electric rm.
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
The US NEC only forbids placing both emergency and non emergency conductors in the same raceway or box. It is silent on separating the raceways so it must be a building code issue.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
#97143 - 01/30/06 06:07 AM Re: emergency electric rm.
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
It is not a building code issue. I think it is fine.
_________________________
Ryan Jackson,
Salt Lake City
Top
#97144 - 01/30/06 12:16 PM Re: emergency electric rm.
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
The IBC Section 302.1.1 covers incidental Use Areas. The only electrical only type incidental use requiring a fire rated barrier wall and floor/ceiling assemblies is for stationary lead-acid battery rooms having a liquid capacity of more than 100 gallons used for facility standby power, emergency power or interrupted power supplies.
These rooms require a 1 hour rating for Group B, F, H, M, S and U occupancies and a 2 hours rating for Group A, E, I and R occupancies.

Other common incidental use areas would be: furnace rooms, boiler rooms, refrigerant rooms, parking garages, incinerator rooms, paint shops, laboratories and vocational shops, also laundry rooms, waste and linen collection rooms and storage rooms over 100 square feet, and padded cells.
_________________________
Earl
Top
#97145 - 01/30/06 12:21 PM Re: emergency electric rm.
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
It may be that your particular electrical room is backed up to a fire area or separation wall. In that case the fire rating will have to extend from floor to ceiling. Any penetrations will have to be closed in a proper manner.
_________________________
Earl
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals