#97066 - 01/19/06 04:30 PM Office receptacle placement
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
I am assuming the 12' rule of the receptacle placement also applies to a commercial office.
And the # of receptacles on a 20A circuit also applies to a commercial office?
Or both of the above are only for a residential setting?

Thank you
Edward
_________________________
Thanks
Edward
Top
2017 / 2014 NEC & Related Books and Study Guides
#97067 - 01/19/06 05:02 PM Re: Office receptacle placement
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
You don't need any receptacles in an office.

Each receptacle in a commercial building counts as 180 VA.

There is no limit to the amount of receptacles on a circuit in a dwelling.
_________________________
Ryan Jackson,
Salt Lake City
Top
#97068 - 01/19/06 06:30 PM Re: Office receptacle placement
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
Thanks Ryan.

So in an office situation there is a limit on #of receptacle per circuit.

Edward
_________________________
Thanks
Edward
Top
#97069 - 01/19/06 06:31 PM Re: Office receptacle placement
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
Doesn't office count as commercial space???

Thanks
Edward
_________________________
Thanks
Edward
Top
#97070 - 01/20/06 05:52 AM Re: Office receptacle placement
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Yes, an office is a commercial space, therefore the 180VA rule of 220.14 applies.

For example, how many receptacles can be on a 20 ampere branch circuit?
20A*120V=2400VA
2400/180=13 devices on a 20 ampere circuit.
_________________________
Ryan Jackson,
Salt Lake City
Top
#97071 - 01/20/06 06:57 AM Re: Office receptacle placement
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
Thanks Ryan
_________________________
Thanks
Edward
Top
#97072 - 01/21/06 09:49 AM Re: Office receptacle placement
XtheEdgeX Offline
Member
Registered: 04/17/05
Posts: 116
Loc: Florida
I thought the spacing was 6', and not 12'.
210.52(A)(1) States the spacing to be 6' instead of 12'. Correct me if I'm wrong.
Top
#97073 - 01/21/06 10:11 AM Re: Office receptacle placement
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
The rule requires that no point on the floor be more than 6' from a receptacle.

If you place the outlets every 12' than no point along the floor line will be further than 6' from at least one receptacle.

Quote:
210.52(A)(1) Spacing. Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 1.8 m (6 ft) from a receptacle outlet.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#97074 - 01/21/06 10:40 AM Re: Office receptacle placement
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
To be clear for everyone reading this thead, the rules in 210.52 only apply to dwelling units. There are no receptacle spacing rules for other occupancies.
Don
_________________________
Don(resqcapt19)
Top
#97075 - 01/21/06 01:26 PM Re: Office receptacle placement
XtheEdgeX Offline
Member
Registered: 04/17/05
Posts: 116
Loc: Florida
OK, I've not been required to do much in the residential area, so I feel kind of dumb here. So what you're saying is, I can measure any place on a floor, any where in the room, and it should be no more than 6' from a receptacle, OR, is it measured any where along the line at the bottom of the wall, even if you measure from one wall across a corner to another wall, should be no more than 6'?
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals