The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 214 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#97066 - 01/19/06 04:30 PM Office receptacle placement
Edward Offline
Member

Registered: 12/14/02
Posts: 309
Loc: California
I am assuming the 12' rule of the receptacle placement also applies to a commercial office.
And the # of receptacles on a 20A circuit also applies to a commercial office?
Or both of the above are only for a residential setting?

Thank you
Edward
_________________________
Thanks
Edward

Top
2014 / 2011 NEC & Related Books and Study Guides
#97067 - 01/19/06 05:02 PM Re: Office receptacle placement
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
You don't need any receptacles in an office.

Each receptacle in a commercial building counts as 180 VA.

There is no limit to the amount of receptacles on a circuit in a dwelling.
_________________________
Ryan Jackson,
Salt Lake City

Top
#97068 - 01/19/06 06:30 PM Re: Office receptacle placement
Edward Offline
Member

Registered: 12/14/02
Posts: 309
Loc: California
Thanks Ryan.

So in an office situation there is a limit on #of receptacle per circuit.

Edward
_________________________
Thanks
Edward

Top
#97069 - 01/19/06 06:31 PM Re: Office receptacle placement
Edward Offline
Member

Registered: 12/14/02
Posts: 309
Loc: California
Doesn't office count as commercial space???

Thanks
Edward
_________________________
Thanks
Edward

Top
#97070 - 01/20/06 05:52 AM Re: Office receptacle placement
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Yes, an office is a commercial space, therefore the 180VA rule of 220.14 applies.

For example, how many receptacles can be on a 20 ampere branch circuit?
20A*120V=2400VA
2400/180=13 devices on a 20 ampere circuit.
_________________________
Ryan Jackson,
Salt Lake City

Top
#97071 - 01/20/06 06:57 AM Re: Office receptacle placement
Edward Offline
Member

Registered: 12/14/02
Posts: 309
Loc: California
Thanks Ryan
_________________________
Thanks
Edward

Top
#97072 - 01/21/06 09:49 AM Re: Office receptacle placement
XtheEdgeX Offline
Member

Registered: 04/17/05
Posts: 127
Loc: Florida
I thought the spacing was 6', and not 12'.
210.52(A)(1) States the spacing to be 6' instead of 12'. Correct me if I'm wrong.

Top
#97073 - 01/21/06 10:11 AM Re: Office receptacle placement
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The rule requires that no point on the floor be more than 6' from a receptacle.

If you place the outlets every 12' than no point along the floor line will be further than 6' from at least one receptacle.

 Quote:
210.52(A)(1) Spacing. Receptacles shall be installed so that no point measured horizontally along the floor line in any wall space is more than 1.8 m (6 ft) from a receptacle outlet.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#97074 - 01/21/06 10:40 AM Re: Office receptacle placement
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
To be clear for everyone reading this thead, the rules in 210.52 only apply to dwelling units. There are no receptacle spacing rules for other occupancies.
Don
_________________________
Don(resqcapt19)

Top
#97075 - 01/21/06 01:26 PM Re: Office receptacle placement
XtheEdgeX Offline
Member

Registered: 04/17/05
Posts: 127
Loc: Florida
OK, I've not been required to do much in the residential area, so I feel kind of dumb here. So what you're saying is, I can measure any place on a floor, any where in the room, and it should be no more than 6' from a receptacle, OR, is it measured any where along the line at the bottom of the wall, even if you measure from one wall across a corner to another wall, should be no more than 6'?

Top
Page 1 of 3 1 2 3 >



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals