The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/08/16 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 214 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#96979 - 01/11/06 01:25 PM Feeder Size
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Can I feed a sub-panel underground in a commercial building with #2 USE-2 aluminum wire connected to a 100amp breaker, under the 2005 NEC?

shortcircuit

Top
2014 / 2011 NEC & Related Books and Study Guides
#96980 - 01/11/06 01:32 PM Re: Feeder Size
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
No.
_________________________
Don(resqcapt19)

Top
#96981 - 01/11/06 01:49 PM Re: Feeder Size
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Violation of 110-14(C)(1)a ?

And the 6ft rule is gone in the 2005 NEC...right

shortcircuit

Top
#96982 - 01/11/06 02:50 PM Re: Feeder Size
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Don- can you elaborate? I agree with part of your answer but the question is not clear if the wiring is outside the building or not.

Also not clear if it's in conduit or not.
Edited for added thought.

[This message has been edited by George Little (edited 01-11-2006).]
_________________________
George Little

Top
#96983 - 01/11/06 04:04 PM Re: Feeder Size
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
George... the wire will be in pvc and the only part "in" the building is where it emerges from the slab to feed the panel...

shortcircuit

Top
#96984 - 01/11/06 04:14 PM Re: Feeder Size
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Umm, how about 310.15 in particular the fact that table 310.16 gives the ampacity of #2AL with 75C insulation and _terminations_ at 90A?

You'd need to jump a couple of hoops to use the 90C column, and 310.15(B)(6) doesn't apply here.

-Jon

Top
#96985 - 01/11/06 04:34 PM Re: Feeder Size
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
The '02 code permits 6 feet of conductor inside the building and the '05 doesn't. That's probaby what Don was getting at and Winnie is right about the ampacity thing. Max overcurrent 90a.
_________________________
George Little

Top
#96986 - 01/11/06 06:25 PM Re: Feeder Size
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Thank you for the feedback...

shortcircuit

Top
#96987 - 01/12/06 08:44 AM Re: Feeder Size
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
My issue is the ampacity of the conductor is 90 amps and cannot be protected by a 100 amp breaker.
Don
_________________________
Don(resqcapt19)

Top
#96988 - 01/12/06 10:23 AM Re: Feeder Size
Helectric Offline
Member

Registered: 01/07/05
Posts: 91
Loc: Brandon, SD
George,

Just curious about why were you were asking if the conductors were inside or outside of the building. Does this matter?

[This message has been edited by Helectric (edited 01-12-2006).]