Can I feed a sub-panel underground in a commercial building with #2 USE-2 aluminum wire connected to a 100amp breaker, under the 2005 NEC?

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#96980 - 01/11/06 01:32 PM Re: Feeder Size
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
No.
_________________________
Don(resqcapt19)
Top
#96981 - 01/11/06 01:49 PM Re: Feeder Size
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Violation of 110-14(C)(1)a ?

And the 6ft rule is gone in the 2005 NEC...right

shortcircuit
Top
#96982 - 01/11/06 02:50 PM Re: Feeder Size
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Don- can you elaborate? I agree with part of your answer but the question is not clear if the wiring is outside the building or not.

Also not clear if it's in conduit or not.
Edited for added thought.

[This message has been edited by George Little (edited 01-11-2006).]
_________________________
George Little
Top
#96983 - 01/11/06 04:04 PM Re: Feeder Size
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
George... the wire will be in pvc and the only part "in" the building is where it emerges from the slab to feed the panel...

shortcircuit
Top
#96984 - 01/11/06 04:14 PM Re: Feeder Size
winnie Offline
Member
Registered: 09/15/03
Posts: 652
Loc: boston, ma
Umm, how about 310.15 in particular the fact that table 310.16 gives the ampacity of #2AL with 75C insulation and _terminations_ at 90A?

You'd need to jump a couple of hoops to use the 90C column, and 310.15(B)(6) doesn't apply here.

-Jon
Top
#96985 - 01/11/06 04:34 PM Re: Feeder Size
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
The '02 code permits 6 feet of conductor inside the building and the '05 doesn't. That's probaby what Don was getting at and Winnie is right about the ampacity thing. Max overcurrent 90a.
_________________________
George Little
Top
#96986 - 01/11/06 06:25 PM Re: Feeder Size
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Thank you for the feedback...

shortcircuit
Top
#96987 - 01/12/06 08:44 AM Re: Feeder Size
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
My issue is the ampacity of the conductor is 90 amps and cannot be protected by a 100 amp breaker.
Don
_________________________
Don(resqcapt19)
Top
#96988 - 01/12/06 10:23 AM Re: Feeder Size
Helectric Offline
Member
Registered: 01/07/05
Posts: 91
Loc: Brandon, SD
George,

Just curious about why were you were asking if the conductors were inside or outside of the building. Does this matter?

[This message has been edited by Helectric (edited 01-12-2006).]
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 90 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 02/21/04
Posts: 1248

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals