The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 186 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#96896 - 01/04/06 04:33 PM Furnace branch circuit
Micmann Offline
Member

Registered: 04/22/05
Posts: 20
I’m wiring some heating equipment in a commercial building. They are two small gas hot air furnaces with A/C coils. The only draw about 2 amps each and then a little more with condensate pumps. Does 422.12 mean I can share a branch circuit for both or that they each need their own branch circuit?

Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#96897 - 01/04/06 04:57 PM Re: Furnace branch circuit
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Exception #2 in that article says to me that it is permissable to do it that way. But why leave it to chance? If it were me I would run (2) 15 amp dedicated branch circuits, one to each unit so if one stops working -- 20 years from now -- the other one will be working, and the customer won't be left without at least some heat, or A/C.

[This message has been edited by ShockMe77 (edited 01-04-2006).]

Top
#96898 - 01/04/06 06:19 PM Re: Furnace branch circuit
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
Or at least ensure that there are two separate disconnects, so you can "drop" one for service and not freeze the occupancy.

Top
#96899 - 01/04/06 06:53 PM Re: Furnace branch circuit
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I agree with Doug. I don't see a problem sharing the circuit but they should have separate disconnects.
_________________________
Greg Fretwell