The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#96733 - 12/21/05 03:54 PM bonding gas line
Trick440 Offline
Member

Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
We have to bond the hot, cold water and the gas line.

If its a 200amp service do I need to use #4 copper or can I just use #6?

Where in the code is this? Thanks
_________________________
Shake n Bake

Top
2014 / 2011 NEC & Related Books and Study Guides
#96734 - 12/21/05 04:00 PM Re: bonding gas line
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
First off you really do not have to make any special effort to bond the gas line, that will be done by the EGC of the equipment connected to the gas line.

As far as the sizes take a look at Table 250.66
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#96735 - 12/21/05 04:22 PM Re: bonding gas line
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Trick, I think you are confusing "bonding" with "grounding."

This is also an area that is usually modified by your local codes, so you will want to check thing out at city hall, as well.

The wire that goes to your ground rod....the "grounding electrode conductor"....is specified by the NEC to need be no larger than #6, without regard to the size of the service. Many places have raised this to a minimum of #4 solid, and further require it be in pipe for extra protection.

Metal parts of the house that are likely to become energised are required to be "bonded" to the system. Such thing include the water line...but the gas service again is an area that local codes differ about. In any event, the NEC specifies a #10 bonding jumper, but many places specify at least a #8 wire be used.

You are no longer allowed to use the water service as a "ground;" you need that ground rod. You are, howerver, required to "bond" the water line.

Top
#96736 - 12/21/05 04:28 PM Re: bonding gas line
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Reno

 Quote:
In any event, the NEC specifies a #10 bonding jumper


 Quote:
You are no longer allowed to use the water service as a "ground;"


I have no idea what you mean with either of those statements.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#96737 - 12/21/05 04:32 PM Re: bonding gas line
Trick440 Offline
Member

Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
Well we ground the water line, but in addition..

We have to have a jumper the connects the cold to the hot and then to the gas line.

We ussually do this at the hot water heater. Thats bonding the gas line isn't it?
_________________________
Shake n Bake

Top
#96738 - 12/21/05 04:56 PM Re: bonding gas line
trekkie76 Offline
Member

Registered: 06/19/04
Posts: 219
Loc: baileyville, maine, usa
I would look at 250.104(b). Now as to what circuit rating to use, not as sure. for a 200 amp it says #6, but is that what would energize it?

Reno, could you elaborate on the water pipe grounding. Is that something in the 2005 NEC?

[This message has been edited by trekkie76 (edited 12-21-2005).]

Top
#96739 - 12/21/05 05:50 PM Re: bonding gas line
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Water Line Service
Grounding Electroide Systems (250.52) Sized per 250.66 (#4) If theres 10 ft. or Metal underground. If not its then its Bonding (See 250.104(A.1))Still sized by 250.66.

Gas piping 250.104B (Other metal Piping)
#6 copper . Unless pipe is grounded by an equipment grounding conductor of a circuit thats using the Gas . The equipment grounding conductor is then an effect bond.

Top
#96740 - 12/21/05 06:38 PM Re: bonding gas line
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Where I am in what has been refered to as the soveriegn city, of the soveriegn state of SF, CA. Water is required as an electrode and/or bond depending on how you look at it, and if a UFER is involved. Water with no UFER, would be supplimented with rods. With a Ufer, which would be full sized, water would be bonded anyway, in the proccess making it an electrode....

Hot to cold at the water heater...

Gas bond, at the second fitting past the meter - required! They'll even let you use the GEC so long as it is not between the electrode and panel.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#96741 - 12/21/05 07:13 PM Re: bonding gas line
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Perhaps I should have said you're not allowed to use the water line as your ONLY ground....250.53(D) ays the pipe shall comply with (1) and (2)...and (2) says the pipe shall be supplimented.
We often forget that there are type of non-conductive pipe that pre-date plastic. Many cities still have wood water mains...and, more recently, WWII started the use of "orangeburg," a pipe made of asphalt-impregnated cardboard.

As far as the bond wire needing to be !0 or larger, I stand corrected....the NEC calls for it to be at least #8. Formerly, this was a local ammendment- it appears that the NEC has caught up! 250.104 is what I am referring to.

Top
#96742 - 12/22/05 02:31 AM Re: bonding gas line
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
To be clear we are required to use a metal water line as an electrode as long as there is 10' of it in direct contact with the earth. It does not matter what is beyond that 10'. An 8' rod is an electrode so it only follows that 10' of metal water line in the ground is an electrode. It will not matter if that 10' of metal line is supplied by non-conductive mains.

In the big picture it may be better if you water line was not electrically continuous with your neighbors.

Yes we must supplement it with one or sometimes two additional electrodes. My guess is that is required as many times people disconnect the GEC from the water line and do not put it back.

I will have to look but I do not believe there is a minimum size bonding conductor for a gas line.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts