The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
sparky 4
Who's Online
1 registered (hyetal), 262 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#96582 - 12/09/05 09:25 AM multiple subpanels
sparky69 Offline
Junior Member

Registered: 12/09/05
Posts: 1
100A residential panel feeding 2 small subpanels. the 2 main lug subs are both fed from a single 2 pole 60A breaker in the mian panel. the 1st sub has wires in from the main and out to the 2nd sub, both wires being under the main lugs. basically the 2 subpanels are paralleled together off the one 60A breaker. is this legal? can the lugs on the 1st sub have 2 wires under them? i beleive they are both 60A subs fed with #6 THHN off the 60A breaker in the main.

2014 / 2011 NEC & Related Books and Study Guides
#96583 - 12/09/05 12:20 PM Re: multiple subpanels
raider1 Offline

Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
If the lugs of the panel were listed for 2 wires, and the OCPD and feeder wires were sized for the load, then there is no violation of the NEC.

This may be a poor design choice but not a NEC violation.


#96584 - 12/09/05 03:56 PM Re: multiple subpanels
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
I agree with Chris, the lugs would most likely be the only problem, but they could probably be changed to a parallel type lug or the #6's could be spliced ahead of the lugs.