#96561 - 12/07/05 05:05 PM bond and/or grounding electrode conductor color
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
The NEC has requirements for the jacket color (if covered) of equipment grounds. However, I can't find any such requirements for bond or grounding electrode conductors. What code reference would keep me from using a pink colored #6 Cu Thhn as a grounding electrode conductor to the water pipe (within 5' of its entrance to 100A serviced home) and then to bond around the water meter with a yellow wire of the same size?

BTW, I used #6 in my example instead of the minimum #8 since it can be run without any protection. I just wanted to state this so that there was no confusion.

[This message has been edited by triple (edited 12-07-2005).]
Top
2017 / 2014 NEC & Related Books and Study Guides
#96562 - 12/07/05 05:18 PM Re: bond and/or grounding electrode conductor color
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Triple, there is nothing prohibiting this as far as the NEC is concerned.

Roger
Top
#96563 - 12/08/05 04:27 PM Re: bond and/or grounding electrode conductor color
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
Thank you Roger for your response.

I'd like to take this question one step further. Obviously I could not use white or gray in the above example since those colors are reserved for the grounded conductor. However, green wire (or black taped green) is often used for the grounding electrode conductor and/or bonding wires. Is this actually NEC compliant? Isn't green technically a color reserved for the equipment ground?
Top
#96564 - 12/08/05 04:40 PM Re: bond and/or grounding electrode conductor color
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
The code did not restrict the use of green for other purposes prior to the 2005 code. In the 2005 code the use of green is restricted to "grounding conductors". That will permits using green for GECs.
Don
_________________________
Don(resqcapt19)
Top
#96565 - 12/08/05 04:41 PM Re: bond and/or grounding electrode conductor color
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Triple:
IMHO, 'green' or grn w/yellow stripe is the designated color for EGC, as well as bare.

As to using any of the above for the bond, I do not know of any NEC Article that would prevent it.

John
_________________________
John
Top
#96566 - 12/08/05 07:08 PM Re: bond and/or grounding electrode conductor color
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I have looked at lots of GECs, they called me the grounding inspector. Green tape over black THHN is the norm if it was insulated at all. That pretty much means it could be any color with green tape. I even think it could be white by the definition of "grounded conductor"
Quote:
Grounded Conductor. A system or circuit conductor that is intentionally grounded.
but the confusion factor would have me asking for a penny's worth of green tape.
_________________________
Greg Fretwell
Top
#96567 - 12/10/05 09:53 AM Re: bond and/or grounding electrode conductor color
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
I made a proposal to the 2005 Code that the GEC be identified in panels and switchboards to reduce confusion.
It was rejected.
Most electricians do this as a good work practice but, it is not required by the Code.
On inspections I "recommend" that the GEC be identified, and usually it is but I can't require it.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.
Top
#96568 - 12/10/05 08:08 PM Re: bond and/or grounding electrode conductor color
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Remember the thread we had going a few years back, regarding the color of the GEC?

It was a very informative thread!

Let me do a search for it, and insert a link.

Scott 35.

----------

***UPDATE***

Found the thread - it's a "Two-Page'r"!

Color Code For GEC in a Main Service Panel
http://electrical-contractor.net/ubb/Forum2/HTML/000956.html

Scott35

[This message has been edited by Scott35 (edited 12-10-2005).]
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#96569 - 12/11/05 04:42 AM Re: bond and/or grounding electrode conductor color
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Quote:
made a proposal to the 2005 Code that the GEC be identified in panels and switchboards to reduce confusion.
It was rejected.


As it shoukd have been. Who exactly was confused?
Top
#96570 - 12/11/05 04:43 AM Re: bond and/or grounding electrode conductor color
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Quote:
I have looked at lots of GECs, they called me the grounding inspector. Green tape over black THHN is the norm if it was insulated at all.

I bet that's not all they called you. What is your basis for requiring this?
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals