#96542 - 12/05/05 04:39 PM Lightbulb Clearance
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Is there a code requirement for the distance that a incandescent type A-lamp would be required to maintain from combustible surfaces such as wood?

For instance, if a 60watt A-lamp, screwed into a keyless lampholder in a basement of a dwelling, was within an inch of a wooden rafter, this would seem to be a hazard.

410.5 gives me some guidance, but is there any other clear guideline that would specify distances from combustible material for type A-lamps?

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#96543 - 12/05/05 05:35 PM Re: Lightbulb Clearance
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Depends on the bulb used...do you have a thermocouple handy?

If I remember correctly, industry standards set 140 degrees F as the maximum temperature a fixture can cause on a "flamable" surface.
Top
#96544 - 12/05/05 06:17 PM Re: Lightbulb Clearance
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
"within an inch of a wooden rafter, this would seem to be a hazard." - Yep....bulb to the side or below, I think it would be too close.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#96545 - 12/05/05 07:00 PM Re: Lightbulb Clearance
jwhite Offline
Member
Registered: 12/01/05
Posts: 64
Loc: Trenton, NC, USA
410.5 Luminaires (Fixtures) Near Combustible Material.
Luminaires (fixtures) shall be constructed, installed, or
equipped with shades or guards so that combustible material
is not subjected to temperatures in excess of 90°C
(194°F).
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 75 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals