#96522 - 12/05/05 01:03 PM What size GEC?
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
If I have a 1000a bus bar service - What size GEC do I need to a qualifying water pipe electrode?
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#96523 - 12/05/05 01:16 PM Re: What size GEC?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Assuming that the calculated load is 1000 amps I would say 3/0 CU

See note 2 to Table 250.66

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#96524 - 12/13/05 04:20 AM Re: What size GEC?
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
This may be a little late but you might consider that the intent of 250.66 is to provide a grounding electrode conductor that has a cir mil area based upon the cma of the supply conductors. In the case described the busbar would be considered the service entrance conductors???


The conversion from area in mils sq to cir mil area is Amil sq divided by .7854.

A 1/4" X 2" bar would have a sq in area in mils of 250 X 2000 or 500,000 sq mils.

divide 500,000 by .7854 to obtain 636,618 + or - cir mil area.

reference to 250.66 and select a 2/0 CU or a 3/0 Al GEC .

Although one could consider busbar as not fulfilling the intent of the term conductor it is conducting material.

just a thought!
Top
#96525 - 12/13/05 05:34 AM Re: What size GEC?
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
There's a question in my mind about what size buss bar is used for a 1000a. Service. I was under the impression that a buss bar .25" x 4" would be used. Using cpal's math the required GEC would be 3/0 cu. or 250 kcmil al.

250 x 4000 =1000000 sq. mils. 1000000/.7854 = 1273236 cir mils. Reference 250.66 would give us a 3/0 cu.

Maybe the question is the physical size of the buss for 1000a. I do agree that it is a conductor.
_________________________
George Little
Top
#96526 - 12/13/05 06:46 AM Re: What size GEC?
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
The Chase Shawmut Book of Electrical Information indicates that a 4" X 1/4" Copper Bar can handel 1000A or 1000 A per Sq"

This information was in the NEC around 1971 or so and it indicated that Copper Bus could carry 1000A per Sq" and Aluminum could handel 700A per Sq"
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals