The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (DanK, LongRunner), 228 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#96334 - 11/19/05 06:44 AM Welding circuit
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
I installed a welding circuit with a 60a breaker in the lower part of a split buss residential panel and put a 70a breaker (max size according to the panel specs) feeding the lower part of a the split buss.
The the welder draws 92 amps max. I didn't want to go over the 70a split buss feeder breaker, so I told the customer he probably couldn't run his welder at maximum without possibly tripping the breaker. Everything is installed up to code, but is this a good idea even being legal?

(This is the same panel I mentioned in the General discussion area about the ("no main disconnect".)
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
2014 / 2011 NEC & Related Books and Study Guides
#96335 - 11/19/05 07:40 AM Re: Welding circuit
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
A lot depends on the duty cycle of the welder. You need to or at least should look at Article 630 which specifically addresses welders.

Welder outlets, the conductors that feed them and the overcurrent protection for them do not follow the 'normal' rules.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#96336 - 11/19/05 11:16 AM Re: Welding circuit
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
I'll check that.
Its a Miller Tig welder
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#96337 - 11/19/05 05:29 PM Re: Welding circuit
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
93Amps would be extremely heavy current for a MIG welder used at a residence. That is most likely an instantaneous value.

If it is a Miller MIG running at 120Volts then 60A is way overkill. Just what kind of plug does it ship with?

Dig into their spec sheet; visit their web page.
_________________________
Tesla

Top
#96338 - 11/19/05 05:48 PM Re: Welding circuit
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Welders get their own section in the NEC. It's worth looking up.

The nameplate will list a "duty cycle." This bit of info in turd is used to select your breaker and wire size. In theory, one could run #12, on a 100 amp breaker, if the duty cycle was low enough.
DOing so would probably be foolish, though. Replace the welder with another machine, and you're likely to have to re-do the entire circuit.

Top
#96339 - 11/20/05 07:45 AM Re: Welding circuit
HLCbuild Offline
Member

Registered: 12/05/04
Posts: 206
Loc: Herndon,Va USA
Have you considered putting the welder breaker in the upper portion of the split buss panel and moving some smaller load down like maybe the water heater or dryer(double 30)to the lower portion?

Top
#96340 - 11/20/05 08:24 PM Re: Welding circuit
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Thats a great idea. Sometimes the obvious just flys right by ya. I check the loads on top.
Thanks,
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top