The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
Yesterday at 09:52 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
1 registered (gfretwell), 0 Guests and 170 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#96236 - 11/10/05 03:36 PM Machinery Ground rods
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
Walked into a plant this afternoon, to quote some work, and I am still noticing guys installing CNC machines, lathes, and such with ground rods by the machines.

I know manufacturers "require" this but the NEC is still somewhat unclear.

Under some excemptions you can put a ground rod if you want but the EGC from the feeder must be tied to it. You can't connect the ground rod by itself to the equipment without that being tied to the service ground.

See where i am going, I hope...

I remove them when I find them, after checking that an EGC was installed.

Am I on the right track?


Dnk.....

Top
2017 / 2014 NEC & Related Books and Study Guides
#96237 - 11/10/05 03:49 PM Re: Machinery Ground rods
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
As long as there is an EGC run with the power conductors and connected to the equipment there is no reason to remove the rods. They do not have any adverse effect.
Don
_________________________
Don(resqcapt19)

Top
#96238 - 11/10/05 03:50 PM Re: Machinery Ground rods
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
If the machine is properly grounded by an equipment ground run with or enclosing the conductors to the machine, then I see no reason to remove the supplementary electrode.

If the rod is required by the installation instructions furnished by the manufacturer of listed equipment, then it is part of the listing and labeling and should remain in place.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#96239 - 11/10/05 03:51 PM Re: Machinery Ground rods
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
As long as the equipment is grounded to the source as required by the NEC they can add as many 'extra pointless' (supplementary) rods at machine.

Quote:
250.54 Supplementary Grounding Electrodes.
Supplementary grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.56, but the earth shall not be used as the sole equipment grounding conductor.


Notice that to the NEC Supplementary is entirely different than Supplemental
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#96240 - 11/10/05 04:10 PM Re: Machinery Ground rods
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
Well, 2 things bother me,
One is the obviuos trip hazzard they posses.
Some of them run across the floor 5-6 feet, to where the ground rod was driven.

The second being, in part to how many I have seen wrong. This is where they didn't pull a EGC, and the ground buss bar inside the equipment was tied to the ground rod only.


Dnk...

Top
#96241 - 11/10/05 04:45 PM Re: Machinery Ground rods
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Quote:
This is where they didn't pull a EGC, and the ground buss bar inside the equipment was tied to the ground rod only.


Keep in mind that an EGC doesn't necessarily have to be pulled.
Conduit also can be considered as the EGC under 250.118. "Wire" is only one of the fourteen acceptable items listed.

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals