The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 221 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#96231 - 11/10/05 01:32 PM reduced neutral conductor
gserve Offline
Member

Registered: 03/11/03
Posts: 92
Is it permissible by code to use an under sized neutral(#4)in a feeder for a mobile home? The reason I ask is because the supply house gave me #2246 feeder cable instead of the usual #2224 and I didn't notice it until the cable was pulled in to the conduit. Code reference please Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#96232 - 11/10/05 02:18 PM Re: reduced neutral conductor
raider1 Offline
Member

Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
Check out 220.22 of the 2002 NEC.

Chris

Top
#96233 - 11/11/05 05:23 AM Re: reduced neutral conductor
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I am curious about the cable being used inside conduit. Is it listed to be used that way and does it have an insulated equipment grounding conductor? Thanks in advance.
_________________________
George Little

Top
#96234 - 11/11/05 01:40 PM Re: reduced neutral conductor
gserve Offline
Member

Registered: 03/11/03
Posts: 92
Yes it is listed that way it is duel rated USE-2 RHH/RHW and the grounding conductor is insulated.Just want to know if a #4 neutral can be used and how to do the math to figure it out. Thanks

Top
#96235 - 11/11/05 07:15 PM Re: reduced neutral conductor
ngoody24 Offline
Member

Registered: 09/25/05
Posts: 34
Loc: pace,FL, United States
to figure your neutral load which tells you your wire size. see section 220.22

Top